I have 11KV/415V power distribution transformer. I have
found unbalance current in LT (415V) side. Also observed
that unbalance voltage (3V) at LV side due to HV side
unbalance voltage. What should I check for this? Also, the
same LV side load can run in balance on captive power.
Answer / k.prakashchandra
Inter -turn short on the HT side is suspected
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the Maximum voltage range for single phase
The ohm is the unit of:(a) Charge(b) Resistance(c) Power(d) Current
How to calculate pitch, gauge of winding wire, and No. of turns for 30HP, 3 phase, 4 poles 50Hz, 380V induction motors
What is the function of a turbo charger in a 1000kva DG set
What is the diffrence between PL Lamps and CFL Lamps
can we make a loop between neutral and body for grounding?
what happen if turbine trip ,g.c.b not open and excitation on condition?
Dyn1 transformer vector group testing how to do
How can calculate ups battery back up time?
25 Answers Cisco, Cooper, Pronet, Wipro,
can you give main difference between ELCB And RCCB?
38 Answers MCB Bank, Reliance, Wipro,
coil is consist of
why we are using the 2 slope in differential relay?but in busbar differential we are using only one slope. what is the reason.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)