How does MCB operate without relay..?
Answers were Sorted based on User's Feedback
Answer / sath
Normally MCB's are used for low voltage application.Phase
line is directly connected to the input pole of MCB.MCB's
are act as a contacter here.In normal operating condition
terminal of the MCB are closed position. if the current
value reach above the rated value then the conduct is open.
so there is no need for the relay here.
| Is This Answer Correct ? | 37 Yes | 12 No |
Answer / victorvgp
simply saying,
RELAY consists of coil wounded on core and a contactor
If you saw a construction of MCB, an arrangement similar to
relay is made with nc contact and an external switch.
During normal operation, current flows through MCB relay
coil is not sufficient to change the position of contactor,
But on faulty condition, the fault current flows through
the MCB relay coil is sufficient to change the position of
contactor as from nc to no.
r u got it.
| Is This Answer Correct ? | 21 Yes | 2 No |
First question itself wrong.MCB contains small relay
mechanism and also a coil.when current flow through coil
beyong the limit the coil will act the mechanish and trips.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / arun gur
MCB (minature ckt breaker)
contains a bymetalic strip which heats up and bend as
current flows through it. the mechanical switch is operated
after it bends above a perticular angle when current flows
beyond the rated current
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / j. r. gaikwad
Relay is name given to a mechanism which changes the
position of a switch under certain predetermined condition
e.g.excess load , excess current , under voltage , over
voltage etc.
MCB contains electromagnet operated switch to trip under
short circuit state ( as it operates insantaneously , this
is necessary under shortcircuit condition ) & a thermal
over load relay i.e. a switch operating because of bending
of a Bimetal strip at higher temp produced by the excess
heat produced by the excess current - due to over load .
MCB simply means "small" circuit breaker .It does contain
mechanism to trip , i.e. switch automatically under adverse
conditions !
This is the right answer.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / durgak
MCB meance Moulded Circuit Breaker also called as miniature
circuit breaker which are small capacity ( low voltage )
breakers and these too are moulded. So MCB is a breaker but
moulded(sealed). The breaker is the term used to a unit
which breaks (opens) the circuit above its rated flow of
current. it has the characteristic and ability to self
operate and isolate(break) the circuit if there is a fault
down the line. Circuit breakers are used to connect the
LOAD to the power circuit(line). Once the breaker has
opened it can not get ON by itself. It is to be actuated
again.Thats why we find a certain breaking capacity value
in MCBs in Kilo Amps.For example for light/fan loads the
MCBs rating is 6Amps which have a breaking capacity of
9Kilo amps whereas power points for ACs need 15Amp MCBs
with breaking capacity of 9 t0 12 Kilo Amps.depends upon
the manufacturers specifications.
As on date best MCBs available in market are:-
MDS,L&T,Siemens. Others of second grade are:-
Havells,Standard,HPL,Indo-Asian.
| Is This Answer Correct ? | 13 Yes | 12 No |
Answer / maddy
I am studying the bimetallic strip used in MCB.
I am trying to theoretically calculate the temperature rise
of the strip when 1.13In (safe value of current for which
the MCB shouldnot trip) is passed through the bimetallic
strip. I am having the dimensions, resistivity, modulus of
elasticity, flexivity, density of the strip.
I even have the practical values with me for ever few
secons of current passed.
I tried to use the relation MC(dT)=I^2Rt
that is all the heat generated is used in the temperature
rise.
But practically other things need to be considered like
heat loss with environment, also the above formula holds
good for only few seconds and here the resistivity I have
taken constant will also vary.
Please help me out with a relevant solution.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / uday
MCB means miniature circuit breaker .it operates on the
basis of relay action .it is provided with a coil connected
directly to the live wire.whenever the faulty current
occures which is greather than normal current thte coil get
energised and pulls the contact.in this manner fault is
isolated.
| Is This Answer Correct ? | 0 Yes | 0 No |
MCB contains metallic conductor, which expand during over
curren or voltage, so the nc becomes no, & the MCB operates.
| Is This Answer Correct ? | 1 Yes | 5 No |
What are objectives of energy managements ?
Why the ceiling fan rotate in anticlock wise direction whereas tables fan rotates at clock wise direction?
Where we use 30mA , 100mA & 300mA RCCB ?
What is hysteresis losses?
all interview questions with answers of ntpc (2000-2009
during installation time of transformer and alternator which points we have to observed?
Dear sir, I am working in wind mill division , pls explain Pls explain in details with formula My question is Wind speed 3.5 M/s Gen RPM is 1500 ( 25 K/w Production ) Wind speed 12 M/s Gen RPM is 1500 ( 220 K/w Production ) Why in 3.5 m/s generation was low , why in 12 m/s generation was high , Pls dont explain wind force or wind density , that one already i know For the above question RPM was same why the KW was different Answer : 1. Its depends on the density ( Force ) of the air Sir , Pls explain wit Formula sir
what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.
if we run a 3 phase machine on two phase what will happend??? given answer with solid reason please
i have a motor 55kw how u will calculate cable specification for this motor
Can we use generator transformer as step down transformer? How?
for 4 MVA , 33K.V/6.6K.V transformer. secondary side the connected load is 3000H.P. What is the rating of capacitor bank to be insttaled.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)