Answer / sath
Normally MCB's are used for low voltage application.Phase
line is directly connected to the input pole of MCB.MCB's
are act as a contacter here.In normal operating condition
terminal of the MCB are closed position. if the current
value reach above the rated value then the conduct is open.
so there is no need for the relay here.
Is This Answer Correct ? | 37 Yes | 12 No |
Answer / victorvgp
simply saying,
RELAY consists of coil wounded on core and a contactor
If you saw a construction of MCB, an arrangement similar to
relay is made with nc contact and an external switch.
During normal operation, current flows through MCB relay
coil is not sufficient to change the position of contactor,
But on faulty condition, the fault current flows through
the MCB relay coil is sufficient to change the position of
contactor as from nc to no.
r u got it.
Is This Answer Correct ? | 21 Yes | 2 No |
First question itself wrong.MCB contains small relay
mechanism and also a coil.when current flow through coil
beyong the limit the coil will act the mechanish and trips.
Is This Answer Correct ? | 12 Yes | 4 No |
Answer / arun gur
MCB (minature ckt breaker)
contains a bymetalic strip which heats up and bend as
current flows through it. the mechanical switch is operated
after it bends above a perticular angle when current flows
beyond the rated current
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / j. r. gaikwad
Relay is name given to a mechanism which changes the
position of a switch under certain predetermined condition
e.g.excess load , excess current , under voltage , over
voltage etc.
MCB contains electromagnet operated switch to trip under
short circuit state ( as it operates insantaneously , this
is necessary under shortcircuit condition ) & a thermal
over load relay i.e. a switch operating because of bending
of a Bimetal strip at higher temp produced by the excess
heat produced by the excess current - due to over load .
MCB simply means "small" circuit breaker .It does contain
mechanism to trip , i.e. switch automatically under adverse
conditions !
This is the right answer.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / durgak
MCB meance Moulded Circuit Breaker also called as miniature
circuit breaker which are small capacity ( low voltage )
breakers and these too are moulded. So MCB is a breaker but
moulded(sealed). The breaker is the term used to a unit
which breaks (opens) the circuit above its rated flow of
current. it has the characteristic and ability to self
operate and isolate(break) the circuit if there is a fault
down the line. Circuit breakers are used to connect the
LOAD to the power circuit(line). Once the breaker has
opened it can not get ON by itself. It is to be actuated
again.Thats why we find a certain breaking capacity value
in MCBs in Kilo Amps.For example for light/fan loads the
MCBs rating is 6Amps which have a breaking capacity of
9Kilo amps whereas power points for ACs need 15Amp MCBs
with breaking capacity of 9 t0 12 Kilo Amps.depends upon
the manufacturers specifications.
As on date best MCBs available in market are:-
MDS,L&T,Siemens. Others of second grade are:-
Havells,Standard,HPL,Indo-Asian.
Is This Answer Correct ? | 13 Yes | 12 No |
Answer / maddy
I am studying the bimetallic strip used in MCB.
I am trying to theoretically calculate the temperature rise
of the strip when 1.13In (safe value of current for which
the MCB shouldnot trip) is passed through the bimetallic
strip. I am having the dimensions, resistivity, modulus of
elasticity, flexivity, density of the strip.
I even have the practical values with me for ever few
secons of current passed.
I tried to use the relation MC(dT)=I^2Rt
that is all the heat generated is used in the temperature
rise.
But practically other things need to be considered like
heat loss with environment, also the above formula holds
good for only few seconds and here the resistivity I have
taken constant will also vary.
Please help me out with a relevant solution.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / uday
MCB means miniature circuit breaker .it operates on the
basis of relay action .it is provided with a coil connected
directly to the live wire.whenever the faulty current
occures which is greather than normal current thte coil get
energised and pulls the contact.in this manner fault is
isolated.
Is This Answer Correct ? | 0 Yes | 0 No |
MCB contains metallic conductor, which expand during over
curren or voltage, so the nc becomes no, & the MCB operates.
Is This Answer Correct ? | 1 Yes | 5 No |
What core magnetic balance test of transformer? How to do this test in a three phase Star star (star-LV, star-HV) transformer? How to measure and where to measure?
EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.
What are the essential characteristics of signal flow graphs?
Explain Need of a starter in a dc motor.? Also explain any two starting and speed control method of dc motor?
What is the difference between Ac curent & DC current
why we testing the core balance of the transformer before comissioning?
1.wat is the negative slip region in the motor?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
State superposition theorem?
define regulation
How many types of instrument cables are there?
State magnitude criterion.