Answer / vinod g
Over load relay is setting normaly at 100% of rated
current, also we can set at reduced current if load current
less and constant.Also overload relay have AUTO & MANUAL
Reset mode. ie in AUTO it get reset automatically with time
delay based on motor temprature reduction. Manual mode we
have to reset on every trip.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / siva24381
First we decide motor full load amphere(or name plate) and
take actual load amphere. If 3HP motor full load amphere is
4.5A but actual load is 3.0A so we set OLR rating 3.5A.
| Is This Answer Correct ? | 0 Yes | 5 No |
Answer / jaspreet singh
over load relay =1.5*full load current.example for 1 h.p
motor takes 1.5 Amp current so its overload relay is setted
at approximate on 2.5 amp
| Is This Answer Correct ? | 1 Yes | 6 No |
Why Transistors are not used as switching devices?
WHAT IS INERTIA,AND WAT IS TORQUE.
My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I - is the value of AC fault current. t - is the operating time of disconnecting device in seconds. K – is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.
why are we adopting 132kv,220kv for transmission rather than using 440kv at all transmission lines as it gives lower losses?
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
Do you need any help with FEWA Electrical Supervisor exams?
what is meant by ceiling voltage, ceiling current?? pl reply asap
why in three phase 440 circuit in all phase current is almost equal L1-35 A,L2-34 A ,L3-31 A but in nutral when i check with clamp meter it shows 25 A?
exact difference between electronicsand electrical
what is mean by D.O. in distribution line poles?
in three pin plug point, whats the reason that one plug point is bigger in size
i want to make an elec generater with only 12v car battery car alternater and 12 volt motor ..... will the battery charge and give power at same time with out over charging the battery?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)