what type of transformer used in soft ware parks its
distribution or power transformer. like 1800 kva
Answers were Sorted based on User's Feedback
Answer / akshay bhat
its Distribution transformer of rating 11000v/433v as per
requirement.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / chandan
its distribution transformer of rating 11000v/433v and KVA
rating is decided by adding all the loads which we intend
to give on the transformer by this we will get total load
and by multiplying that load to power factor we wil get KVA
rating of the transformer.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / natarajan
Depend upon the harmonics converter transformer is used
Is This Answer Correct ? | 1 Yes | 0 No |
what is 3rd Harmonics? how it is generated in alternator
Phase control and integral control are used for?
HOW MANY EARTHINGS REQUIRED FOR GENERATER
Differentiate between real and apparent power?
Can 60 Hz transformer be used inplace of 50 hz transfromer?
IC 741 is opampIC..moreover AND OR NOT ICs also have '74' in them.. why is that number specifically used?
1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
16 Answers Ecil, Engineers India, MahaDiscom,
why we use only sine wave in ac why we do not use other wave forms
kVA rating of open delta connected transformer is _____% kVA rating of delta/delta connection A 50 B 70.7 C 57.7 D 75.7
What are the usege & different between UPS & batteries with charging system in in Substation?( UPS 120V AC & battery charger is 120v DC)
3ph motor running with unequal kw and different pf what are the reasons
What could be the problem if two power transformers trip on stand by earth fault at same time