DIFFERENCE BETWEEN POWER AND CONTROL CABLES
Answers were Sorted based on User's Feedback
Power cable mainly intend to use transfer of power,
specifically current, over a defenite length.
According to the rating there will be change in the no. of
starnds etc for a.c.
control cables are mostly paired cables ,sometimes more
flexible than power cable. and are not intend to carry more
than 10A.(max.).
Is This Answer Correct ? | 39 Yes | 5 No |
Answer / shahulsnfa
there are voltage levels in power transfer.. two types of
voltage is there, one is control voltage and power voltage.
control voltage starts from (0-230), power voltage from
0 - 433kv.. so depending upon the application we are
distinguishing.. even the same 230 v can be used as control
as well as power voltage also....
Is This Answer Correct ? | 22 Yes | 6 No |
Answer / parminder singh
Control cable are very much flexible than power cables.
power cables have high tensile strength than control cables.
power cables used for high power transfer from one side to other
control cables use 230v maximum
Is This Answer Correct ? | 32 Yes | 19 No |
Answer / kanungo
A POWER CABLE CAN BE OF MAXIMUM 4 CORE ONLY BUT OF ANY SIZE
DEPENDING UPON THE CURRENT CARRYING REQUIREMENT.
A CONTROL CABLE CAN BE OF ANY NO. OF CORES BUT USUALLY TO
CARRY CURRENT UPT0 10AMPS
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / sanjay bhushan
1. Power Cables having more size than control cables
2. power cables used for direct High voltage power.
3.Control cables used for wiring in control panels,
controling divices.
4.Power cables having more dia. than control cables.
5 Power cables requires cable terminal kit & control cables
didnt requires of it.
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / tarun aggarwal
the power which is gernated in a station has high potential
and are transmitted by power cable like aac acsr etc which
have large diameter or high no.of strands. while control
cables are used in stations to control various activities of
equipments in stations like colling fan scontrols panel etc
in hydro plants also they are more flexible
Is This Answer Correct ? | 13 Yes | 8 No |
According to cable types and size
1Cx2.5sq.mm to 4CxMax. Sq mm - Power cables
3Cx1.5sq.mm to 27Cx2.5sq.mm-Control Cables
Control Cables are available in 1.5sq.mm and 2.5sq.mm-Only
in Cu.
Power Cables are available from 1Core to 4Core and 2.5sq.mm
to 630sq.mm in Al. and Cu
Power cable is connecting the Power circuit. whereas control
cables is connecting the control circuit.
Is This Answer Correct ? | 18 Yes | 13 No |
Answer / dinesh kakatkar
for the control of any circui few amperes of current is
required so normally we use a small cross-sectional wires.
This current can be mA to Few Ampers and risk of FAULT
current flowing is less and normally a single phase so we
require a small cable of 2 core or 3 core or less cross-
section.
The power cables is used depending on the application in
the Amperes to KA and the FAULT current is more and in the
range of KA.So the application of this cable is to supply a
several Ampere of current and Voltage ranging from the 230
V to Several KV depending on the load.So this cable is
called power cable as it is used to feed power.
Even based upon the application the cables are called as
Power and Control Cables.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / dilip ghodake
power cabels are carrying power and control cables are to
control the power.
Is This Answer Correct ? | 4 Yes | 17 No |
what happens if i connect acapacitor to a generator load
ELECtrical
2 Answers Bahwan Engineering, Bhel, Electrosteel, NBCC, Qatar Airlines,
what is need of air gap in expansion section in busbar?
how many earthings will be required for 1 isolator & 2 VCB, which are connected to a 1600 KVA Distribution TRansformer?
What, in the construction of a transformer, controls KVA? For example 600/208/120 V transformer can be 10kVA or 45kVA!!! What do we change in the construction of a Transformer in order to change the rating but not the voltage.
can we ran equipment up to 10kw between phase to grounding/ earthing. beside above can we use grounding instead of neutral. .
1 Answers TNEB Tamil Nadu Electricity Board,
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
What is the effect of interchanging core(made of steel) and winding(made of copper) material in case of transformer? Give proper explanation in regard to different losses in transformer.
for a 400kv t/m line with 10 ampere current will corona occur?
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV is ok ,but haw to calculate the KA rating?
what is brushless generator.How does work it..??
I have applied the post Junior Engineer-iii(c&w)in R.R.B chennaI recently . can i get any model question paper LAST 4 YEARS?
2 Answers Data Entry Operator, RRB, SSC,