Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to do CT Burden test

Answers were Sorted based on User's Feedback



how to do CT Burden test..

Answer / kay pee corporation

When a CT is used in a metering circuit it will have a
secondary current loop connecting its output through a test
block to a meter . This current loop will consist of a
secondary wire from its X1 terminal to a test block and go
through a shorting switch. From the shorting switch the
current loop will have a wire connection over to the meter,
go through the meter, and have a wire connection back to
the test block. From there the current loop will go through
the secondary current test switch and have a wire
connection return to the X2 terminal of the CT with a
connection to neutral either at the output of the current
test switch or at the X2 terminal of the CT . This
secondary current loop has an electrical impedance called
its burden. This burden will have a resistance component
and may have an inductance component. Usually the
inductance component is small and is treated as negligible.
The burden of the secondary circuit, as installed, is
designated the natural burden of the circuit. If installed
properly the natural burden should be less than a few
milliohms. The CT is designed to operate accurately under
certain burden conditions as specified. The accuracy class
certification of a CT is presented for a stated upper value
of burden, called the CT’s rated burden. For example it may
have an accuracy class of 0.3 for burden of 1, meaning that
the CT’s rated burden is 1 ohm and the CT will maintain
accurate rated ratio performance within 0.3 percent for
secondary circuit burdens up to 1 ohm. This rated burden
classification is also stamped on the CT nameplate. If the
natural burden of the secondary circuit is larger than the
rated burden, then the CT is not certified to have accurate
performance. For this condition, called over-burdened, the
secondary current will not be accurate tending to be
somewhat less to significantly less than the accurate value
causing the metering to be in error in favor of the
customer. Furthermore, secondary circuits may have burden
build up as they age due to loose connections, corrosion,
broken stranded wires, etc. CT’s, as installed, need to
have enough excess burden capacity over the natural burden
to allow accurate performance over time even if there is
additional burden build up in the secondary circuit.

Is This Answer Correct ?    3 Yes 2 No

how to do CT Burden test..

Answer / saad

thats CT saturate voltage thats we can see in the table to
decide the CT size and accuracy the formula for calculate

total resiatance * Fault current
Voltage at the time of fault-------------------------
CT ratio
For example that voltage 34Volts and the ct saturate
voltage 40Volts thats a knee point so we select a ct that
have less than 40volts

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

What is touch potential and step potential?

0 Answers   IRI,


How Earthing is prevents shock?Explain

4 Answers  


when is the Ohms law is applicable?

11 Answers   ABB,


which one has maximum efficiency autotransformer or transformer?? and why??

2 Answers  


what is the difference between static and dynamic induced emf?

14 Answers   College School Exams Tests, MRF, Suraj Constructions,


How much should be the specific gravity of a DG set battery Electrolyte.

2 Answers  


Name the different control schemes of electric rive.

1 Answers   DVC,


can transformer of different kvas be paralled

2 Answers  


Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?

0 Answers  


how to calculate full load current of transformer & induction moter ?

2 Answers  


will 1050kva DG set withstand for back charge of 16MVA transformer

0 Answers  


1. what is the power factor and whatis his losses 2. what is the working procedure of 51RNB AND 87 relay

3 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)