how to do CT Burden test
Answers were Sorted based on User's Feedback
Answer / kay pee corporation
When a CT is used in a metering circuit it will have a
secondary current loop connecting its output through a test
block to a meter . This current loop will consist of a
secondary wire from its X1 terminal to a test block and go
through a shorting switch. From the shorting switch the
current loop will have a wire connection over to the meter,
go through the meter, and have a wire connection back to
the test block. From there the current loop will go through
the secondary current test switch and have a wire
connection return to the X2 terminal of the CT with a
connection to neutral either at the output of the current
test switch or at the X2 terminal of the CT . This
secondary current loop has an electrical impedance called
its burden. This burden will have a resistance component
and may have an inductance component. Usually the
inductance component is small and is treated as negligible.
The burden of the secondary circuit, as installed, is
designated the natural burden of the circuit. If installed
properly the natural burden should be less than a few
milliohms. The CT is designed to operate accurately under
certain burden conditions as specified. The accuracy class
certification of a CT is presented for a stated upper value
of burden, called the CT’s rated burden. For example it may
have an accuracy class of 0.3 for burden of 1, meaning that
the CT’s rated burden is 1 ohm and the CT will maintain
accurate rated ratio performance within 0.3 percent for
secondary circuit burdens up to 1 ohm. This rated burden
classification is also stamped on the CT nameplate. If the
natural burden of the secondary circuit is larger than the
rated burden, then the CT is not certified to have accurate
performance. For this condition, called over-burdened, the
secondary current will not be accurate tending to be
somewhat less to significantly less than the accurate value
causing the metering to be in error in favor of the
customer. Furthermore, secondary circuits may have burden
build up as they age due to loose connections, corrosion,
broken stranded wires, etc. CT’s, as installed, need to
have enough excess burden capacity over the natural burden
to allow accurate performance over time even if there is
additional burden build up in the secondary circuit.
| Is This Answer Correct ? | 3 Yes | 2 No |
thats CT saturate voltage thats we can see in the table to
decide the CT size and accuracy the formula for calculate
total resiatance * Fault current
Voltage at the time of fault-------------------------
CT ratio
For example that voltage 34Volts and the ct saturate
voltage 40Volts thats a knee point so we select a ct that
have less than 40volts
| Is This Answer Correct ? | 0 Yes | 1 No |
Hi Suppose we have a wye/wye transformer which is grounded at both sides,in this situation, do we have ay ground transformer? in other words, ground transformer can do any thing more (while we have nuetral wire in both sides)? As the last question, what about 3rd harmonic? we have two choices: first using wye/delta transformer + ground transformer and second using wye/wye earthed connection.in the former choice, we dont have 3rd harmoonic at the secondary side but what about Yn/yn conection? do we suffer from 3rd harmonic in the Yn/yn connection?
A current of 2A flows for 10 hour through a 100 ohm resistor. The energy consumed by the resistor is:(a) 0.5 kWh(b) 4 kWh(c) 2 kWh(d) 0.02 kWh
Which transformer is suitable for 220/11 kV, 60 MVA, distribution , Y-Y or D-Y or Y-D, give comparison for the same.
What is star-delta transformer?
why the transformer secondary voltage is more than the load end voltage like t/f 11KV/433V for 415V(terminal voltage)
Whether the Dc motor Droping the power factor like AC motor if lot of motor running in factory is it necessary to connect capacitor bank
HOW TO DRAW THE VECTOR DIAGRAMS OF A Dyn 11,YdN 1 transformers?
what is power factor
In D O l starter motor starts as a star connected ,then in star delta starter also motor initially starts as star how come star delta is preferred from dol
in 33/11kv stepdown transfomer, transformer will stepdown to 11kv & remaining 22kv where it will go..
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
explain Density
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)