Is it possible that Generator trip but Turbine not trip.Give
explanation.
Answer / k.prakashchandra
It happens if turbine trip circuit is not connected to
master trip relay.If the generator trips alone on load , the
turbine may trip due to over speed.
| Is This Answer Correct ? | 3 Yes | 1 No |
what is JE exam?
I have 30 kw motor load & i have selected 10 kvar capacitor bank for power factor improvement.my existing p.f is 0.85 & proposed p.f is 0.99 so ,is it right selection? 2 nd question how to connect c.bank whether in delta or star connection & how to decide it?
Can you any one explain different between instantaneous over current and IDMT
how to find out speed of single phase motor
what is the difference between synchoronous and alternator and induction motor and generator
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
what are all the daily preventive maintainance carried out in transformer?
What is a captive power plant?
Why we use d.c. meger in a.c. induction motor?
hr round
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
Earth has zero potential then what would be the neutral potential ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)