What is mean by INRUSH CURRENT?
Answers were Sorted based on User's Feedback
Answer / kalirajan.n
Inrush current or input surge current refers to the maximum,
instantaneous input current drawn by an electrical device
when first turned on. For example, incandescent light bulbs
have high inrush currents until their filaments warm up and
their resistance increases. Alternating current electric
motors and transformers may draw several times their normal
full-load current when first energized, for a few cycles of
the input waveform. Power converters also feature high
inrush currents relative to their steady state currents
Is This Answer Correct ? | 21 Yes | 1 No |
Answer / kapil mishra
inruse current always occurs in inductive coil like
transformer, reactor during charging . it happens due to
non availability of back e.m.f. . inrush current is
praporsanal to V -E/R+X .
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / bhavin
When a transformer is first energized a transient current
much larger than the rated transformer current can flow for
several cycles. This is caused because the transformer will
always have some residual flux density and when the
transformer is reenergized the incoming flux will add to
the already existing flux which will cause the transformer
to move into saturation.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / atul rastogi
Inrush current is the current drawn by the load at the time
of switching. It depends upon starting impedence of the
load as some load have changing impedence depending upon -
temp., fr. etc.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / subra
During the staring period The electrical equipments are taking more current example aircondion units, lifts , transformers,chillers etc
this may be 6 times of the ratedcurrent
this instantanious current is called inrushcurrent
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / chandan
inrush current means the starting current of a transformer or a motor.During starting, the inductive equipment draws huge current from its source.There is 2nd,3rd,4th and so on harmonics frequency currents are present with the fundamental frequency during the charging of the equipment.Specially ,2nd harmonic currents are predominantly present during the starting or charging of the equipment.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dolnarayan patel
Flow of heavy current for short duration.
Is This Answer Correct ? | 1 Yes | 11 No |
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?
why use in & out Diesel line in dg set.
if a 3 point starter is not available, how can a dc motor be started?
3 Answers Accenture, BIT, Techno Solutions,
any one have papers of hpcl or sailof ELECTRICAL ENGG.
WHAT IS MEANT BY TV TERMINAL IN 500MVA TRANSFORMER?
Why does amplifier gain reduce?
what is the main function of capacitors in mccs.
Why transformer making sound during operations?
a 100mva,400/200v transformer has leakage impdce of 10% draws a steady state line currentof---------------
what is ballast
what is mean by PIR in circuitbreaker and give me detail of that?
What Factors should we consider while synchronizing two DG Sets?