Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is the difference between CT for protection and Ct for
metering?

Answers were Sorted based on User's Feedback



What is the difference between CT for protection and Ct for metering?..

Answer / mahesh

Metering ct needs high accuracy(ie,value of metering ct should be small 0.1,0.2,etc.,) than protection ct ie, metering ct accuracy class will be=0.1,0.2,0.5,1,3 and 5
eg;
The accuracy class of measuring or metering CT is 0.1, means the maximum permissible limit of error is 0.1%, more clearly, if we try to measure 100 A with a 0.1 class CT, the measured value may be either 100.1 or 99.9 A or anything in between these range.

for protection CT the accuracy class is low (ie, value of protection ct should be high 5P,10P,15P)

Is This Answer Correct ?    3 Yes 5 No

What is the difference between CT for protection and Ct for metering?..

Answer / raja

Protection CT will be more sensible then Metering CT

Is This Answer Correct ?    1 Yes 5 No

What is the difference between CT for protection and Ct for metering?..

Answer / mulengal

by design protection cts have lower burden which allows for
higher fault currents while metering cts have higher burden
which allows for accuracy

Is This Answer Correct ?    12 Yes 38 No

What is the difference between CT for protection and Ct for metering?..

Answer / kadiresan.k

Generally CT is used to measure higher currents, We need
both Metering and Protection CTs seperately with different
class of accuracy. The purpose of metering CT is to read
the actual current, so it has less class of accuracy.
Whereas in case of protection CT, The measured value of
current is used to protect the equipment by identifying the
abnormalities at the initial stage itself, (provided the
protection relay is tuned perfectly)and protects the
equipment(motors/transformers/transmission and distribution
systems)So it needs high accuracy than metering CTs.

Is This Answer Correct ?    41 Yes 77 No

What is the difference between CT for protection and Ct for metering?..

Answer / minal

ct for protection means that current transformer is used to
step down the higher values of current to lower values
which is to be measured by the instruments.Thus it protects
the equipment from damages.
ct is also used to measure the low values of current.This
is how it is used for metering.

Is This Answer Correct ?    14 Yes 124 No

What is the difference between CT for protection and Ct for metering?..

Answer / infodoss

CT is used to measure the transmission current.
Transmission currents are very high so cannot messure
directly.first to step down the current and then measure
the current using some ratio.CT protection is used to
avoide the aceident and eleminating losses.

Is This Answer Correct ?    37 Yes 153 No

Post New Answer

More Electrical Engineering Interview Questions

Any body can help me in getting LT panel test procedure.

0 Answers   TATA,


what is function of centrifugal switch in single phase induction motor..?

3 Answers  


Is MV canble armour can be earthed at both ends?

2 Answers  


how does this job compare with others you have aplied for?

0 Answers  


What is the principle of HIGH SPEED DIRECT DRIVE MOTOR ?

0 Answers   Honeywell,


What is Neutral Transformer? what is the use of this?

4 Answers  


What are the loading factors to be considered for transformer sizing/selection?

3 Answers  


If the output of a 100kva, 415v generator is stepped up to 11kv with a 500kva transformer,can the transformer be Loaded above the source generator loading?

2 Answers  


difference bteween neutral grounding resistor and neutral grounding transformer??

1 Answers  


Why are tertiary windings used in transformers?

2 Answers  


SSC JE ELECT.

1 Answers   CPWD, SSC,


what are the various types of towers used in transmission line

12 Answers   Power Grid, UltraTech,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)