What is the difference between CT for protection and Ct for
metering?
Answers were Sorted based on User's Feedback
Answer / mahesh
Metering ct needs high accuracy(ie,value of metering ct should be small 0.1,0.2,etc.,) than protection ct ie, metering ct accuracy class will be=0.1,0.2,0.5,1,3 and 5
eg;
The accuracy class of measuring or metering CT is 0.1, means the maximum permissible limit of error is 0.1%, more clearly, if we try to measure 100 A with a 0.1 class CT, the measured value may be either 100.1 or 99.9 A or anything in between these range.
for protection CT the accuracy class is low (ie, value of protection ct should be high 5P,10P,15P)
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / raja
Protection CT will be more sensible then Metering CT
Is This Answer Correct ? | 1 Yes | 5 No |
Answer / mulengal
by design protection cts have lower burden which allows for
higher fault currents while metering cts have higher burden
which allows for accuracy
Is This Answer Correct ? | 12 Yes | 38 No |
Answer / kadiresan.k
Generally CT is used to measure higher currents, We need
both Metering and Protection CTs seperately with different
class of accuracy. The purpose of metering CT is to read
the actual current, so it has less class of accuracy.
Whereas in case of protection CT, The measured value of
current is used to protect the equipment by identifying the
abnormalities at the initial stage itself, (provided the
protection relay is tuned perfectly)and protects the
equipment(motors/transformers/transmission and distribution
systems)So it needs high accuracy than metering CTs.
Is This Answer Correct ? | 41 Yes | 77 No |
Answer / minal
ct for protection means that current transformer is used to
step down the higher values of current to lower values
which is to be measured by the instruments.Thus it protects
the equipment from damages.
ct is also used to measure the low values of current.This
is how it is used for metering.
Is This Answer Correct ? | 14 Yes | 124 No |
Answer / infodoss
CT is used to measure the transmission current.
Transmission currents are very high so cannot messure
directly.first to step down the current and then measure
the current using some ratio.CT protection is used to
avoide the aceident and eleminating losses.
Is This Answer Correct ? | 37 Yes | 153 No |
Hot Water System (HWS). Will a 30ma elcb have more nuisance tripping than 100ma elcb
Name the types of motors used in vacuum cleaners, phonographic appliances, vending machines,refrigerators, rolling mills, lathes, power factor improvement and cranes.
what is the use of CAPACITOR in CFL lamp?
in alternator permanent magnet generator is also connected on the alternator shaft,then y that PMG voltage is very low as compared to alternator?
iam preparing for rrb section engineer post in electrical branch.suggest the right textbook for my reference.fromwhere i will get the previous q.papers?
What is the difference between Encoder and Resolver?
If the Power Factor of generator is 0.85...What does this mean and Can the motors connected to this generator operate at PF more than 0.85 ?
How to work to the x'mer as a induction motor?
What is cogging and crawling phenomenon in motor.
how we can improve power factor from 0.8 to 0.85 or 0.9 & how we identify its either lag or lead ? thank you
Which type of questions well asked. ?
What are differences between Conventional & Addressable type smoke detectors?