Why the transformer rating is denoted in VA rating why not
in KW

Answers were Sorted based on User's Feedback



Why the transformer rating is denoted in VA rating why not in KW..

Answer / manish kumar meena

in transformer cu loss depends on current and iron loss on
voltage.Hence total loss depends on volt-ampere(VA) and not
on phase angle between voltage and current.Thats is why
rating of transformer is in KVA.

Is This Answer Correct ?    58 Yes 5 No

Why the transformer rating is denoted in VA rating why not in KW..

Answer / annakka

the power factor of the loads connected in transformer are
not same.

Is This Answer Correct ?    18 Yes 2 No

Why the transformer rating is denoted in VA rating why not in KW..

Answer / sanket patil

THE POWER FACTOR OF A TRANSFORMER FEEDING THE LOAD
DEPENDS ON THE NATURE OF THE LOAD; HENCE THE ACTIVE(P) AND
REACTIVE(Q) POWERS SUPPLIED BY THE TRANSFORMER MAY CHANGE
FOR A FIXED APPEARENT POWER(S).
HENCE THE TRANSFORMER RATING IS ALWAYS SPECIFIED IN KVA
AND NOT IN KW OR KVAR AS THEY CHANGE AS PER THE LOAD
CONNECTED TO THE TRANSFORMER.

Is This Answer Correct ?    14 Yes 5 No

Why the transformer rating is denoted in VA rating why not in KW..

Answer / mukund

The KW rating is assigned for equipments that consumes power with certain leading/lagging between Voltage and Current depending on the nature of the load (A resistive load is more towards V&I in sync whereas an inductive load has V&I lagging and A capacitive load featuring V&I leading). A transformer is supposed to only transfer the power, although there are inherent losses while doing the same, however for practical purposes, eliminating transformer's own consumption, a transformer is rated on its original purpose with the simple V&I relationship disregarding the Cos-phi factor (the lead/lag of V&I). Hope I am making some sense

Is This Answer Correct ?    3 Yes 3 No

Why the transformer rating is denoted in VA rating why not in KW..

Answer / mahantesh

IN TRANSFORMER THERE ARE MANY LOSSES AS CORE LOSS ,OHMIC
LOSS WINDAGE N FRICTIONAL LOSS ETC.....THE CORE LOSSES ARE
PROPORTIONAL TO VOLTAGE AND OHMIC LOSSES ARE PROPORTIONAL TO
CURRENT THAT'S THE MAIN REASON WHY TRANSFORMER ATING IS IN KVA.

Is This Answer Correct ?    0 Yes 0 No

Why the transformer rating is denoted in VA rating why not in KW..

Answer / robert harper (ee tech)

KW=work
VA=ability to do work, no power factor considered.

Is This Answer Correct ?    5 Yes 6 No

Why the transformer rating is denoted in VA rating why not in KW..

Answer / chandrashekhar sahu

The rating of any machine depends on the factor that always
remain same at any condition. In case of a transformer the
multiplication of voltage and current for primary and
secondary side remain the same at all load conditions. so
the transformer rating denoted as VA.

Is This Answer Correct ?    7 Yes 16 No

Post New Answer

More Electrical Engineering Interview Questions

what will happen if i connect the buchholz relay in reverse direction.

1 Answers   MAN,


1)Explain why the cradle guard is used on railway crossing in overhead line construction?

0 Answers  


why the NGR (neutral grounding resistor) always OFF during DG off?

0 Answers   Bhel,


what would happen if u assume to insulate all the overhead lines and no insulators....??do you think it to b an advantag or a disadvantage??justify.

3 Answers  


What are the minimum acceptable insulation resistances of insulation of underground cable suitable for 0.440kV,11kV, 33kV and 66kV?

2 Answers  


is there any chart showing the suitable cable size according to AMP and length ? for three phase motors

0 Answers  


when we see the lube oil grade its 15w/40 or 20w/40 in this what is W Explain breifly

1 Answers  


What mean 150 amp hour write on battery.

1 Answers   Syncom,


hi how are you? i m in walchand college of engg. do you have interest in join me through email so send your email id

0 Answers  


Which motor has high Starting Torque and Staring current DC motor, Induction motor or Synchronous motor?

5 Answers   BSL, Elite, TTA,


sir i am ece engineer.i want to job in power plant.what is the best option for me as electrical engineer or instrumentation engineer?pls reply me.

1 Answers  


one split ac how can told of this ac which Tr tell me us

0 Answers   Wipro,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)