Why the transformer rating is denoted in VA rating why not
in KW
Answers were Sorted based on User's Feedback
Answer / manish kumar meena
in transformer cu loss depends on current and iron loss on
voltage.Hence total loss depends on volt-ampere(VA) and not
on phase angle between voltage and current.Thats is why
rating of transformer is in KVA.
| Is This Answer Correct ? | 58 Yes | 5 No |
Answer / annakka
the power factor of the loads connected in transformer are
not same.
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / sanket patil
THE POWER FACTOR OF A TRANSFORMER FEEDING THE LOAD
DEPENDS ON THE NATURE OF THE LOAD; HENCE THE ACTIVE(P) AND
REACTIVE(Q) POWERS SUPPLIED BY THE TRANSFORMER MAY CHANGE
FOR A FIXED APPEARENT POWER(S).
HENCE THE TRANSFORMER RATING IS ALWAYS SPECIFIED IN KVA
AND NOT IN KW OR KVAR AS THEY CHANGE AS PER THE LOAD
CONNECTED TO THE TRANSFORMER.
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / mukund
The KW rating is assigned for equipments that consumes power with certain leading/lagging between Voltage and Current depending on the nature of the load (A resistive load is more towards V&I in sync whereas an inductive load has V&I lagging and A capacitive load featuring V&I leading). A transformer is supposed to only transfer the power, although there are inherent losses while doing the same, however for practical purposes, eliminating transformer's own consumption, a transformer is rated on its original purpose with the simple V&I relationship disregarding the Cos-phi factor (the lead/lag of V&I). Hope I am making some sense
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / mahantesh
IN TRANSFORMER THERE ARE MANY LOSSES AS CORE LOSS ,OHMIC
LOSS WINDAGE N FRICTIONAL LOSS ETC.....THE CORE LOSSES ARE
PROPORTIONAL TO VOLTAGE AND OHMIC LOSSES ARE PROPORTIONAL TO
CURRENT THAT'S THE MAIN REASON WHY TRANSFORMER ATING IS IN KVA.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / robert harper (ee tech)
KW=work
VA=ability to do work, no power factor considered.
| Is This Answer Correct ? | 5 Yes | 6 No |
Answer / chandrashekhar sahu
The rating of any machine depends on the factor that always
remain same at any condition. In case of a transformer the
multiplication of voltage and current for primary and
secondary side remain the same at all load conditions. so
the transformer rating denoted as VA.
| Is This Answer Correct ? | 7 Yes | 16 No |
HOW DOES THE FAN REGULATOR CONTROLS ITS SPEED
Diff between power trans and generating transformer?
What are the roles and responsibilities of electrical engineer in cement plant
why the transformer connected like STAR- STAR, DELTA- DELTA, STAR- DELTA, DELTA-STAR ...? why these connections ,,, explain the advantages these connections?
What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?
what is rated speed?
why neutral should connect to earth in delta-star type transformer
what is appearent power?
what is the value of the earth resistance in mositure place
After completing iti in electrician, how can i get certificate of electrical supervisor? What ia requirements. For it?
In 3.5X150 Sq.mm cable what does 150 stand for outer dia or inner dia?
what curve and rateing would you use for a three phase 0.75kw motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)