What are methods to avoid the inrush current at the time of
starting of power transformer ?

Answers were Sorted based on User's Feedback



What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / suresh kumar

We cannot avoid inrush current when any transformer is
switched on after a long period of shutdown. Only thing we
can do is minimising it by charging the transformer by the
lowest voltage (using tapp changers)and we can avoid
spurious tripping by inrush current by using only
transformer differential relays in which an inrush current
filter is used.

Is This Answer Correct ?    15 Yes 1 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vinothbabu.k

BRFORE STARTING ON THE TRANSFORMER WE SHOULD SWITH OFF ALL
THE OUTGOING FEEDER FROM THE DISTRIBUTED PANEL BOARD,THEN
ON THE TRANSFORMER WITHOUT CONNECTING ANY LOAD, THEN SWITH
ON THE FEEDER ONE BY ONE,R CONNECTED LOAD.THIS THE METHOD
TO AVOID THE INRUSH CURRENT FROM THE TRANSFORMER...

Is This Answer Correct ?    13 Yes 4 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / mukhesh

their is no chanses to avoid the magnetic inrush currents
in p t/f by wn inrush curens come the t/f will doing the
vibrations to avoid vibrations steel chains are fixced

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / makku

we can reduse inrush currrent by using winding having high reactance

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / priyan

You can reduce the second harmonic by using the DELTA
connection in the CT’s but I prefer to play with the
protection relay parameters, in this case it is better to
control the differential current, there is 2 slopes for the
differential zones, try to increase the slope N01 to get
passing the inrush current.
By filtering the 2 nd harmonics, refer to relay co
ordination and set the values

Is This Answer Correct ?    1 Yes 2 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vijay

apply a coil before applicable circuit

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / karthikeyan

Its recommended to install an CLR (Current Limiting Reactor)
befroe the Power Transformer to reduce the inrush current.

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / a.kossay

TO AVOID INRUSH CURRENT IN TRANSFORMER WE MUST USE A
VOLTAGE SENSE RELAY TO MONITOR THE VOLTAGE PEAK , SO WHEN
ITS VOLTAGE PEAK THE C.B CAN BE CLOSED AND INRUSH CURRENT
WILL BE LIMITED

Is This Answer Correct ?    1 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

If two generator running parallel, at that condition both ngr Taken in line or taken any one ngr, but why any one or both Ngr in line? Ngr is use for which purpose?

3 Answers  


What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)

17 Answers   Alstom, Call Centre, EDC, HCL, Procon Engineers,


What is the difference between earth and neutral

4 Answers   ABB, Tamboli Engineers,


what is meant by 2 within a star in a voltmeter dial?

0 Answers  


What facility we get after CT secondary earthing and how?

0 Answers   Reliance,






Can double compression glands be used with regular cables?

0 Answers  


what is the profesional board for electrical engineer what is thepast and during construction for electrical engineering

0 Answers  


1.why motor rating in kw instead of KVA? 2.why alternators rating in KVA instead of KW?. 3.why transformer rating in KVA instead of KW?.

6 Answers  


HOW THE OLTC TRANSFORMER SAVE ENERGY IN COMPARISON TO OFF LINE TRANSFORMER AND IS IT ECONOMICAL TO REPLACE THE OFF LINE TRANSFORMER TO OLTC TRANSFORMER

0 Answers  


Is it required to lay GI wires along with GI/MS conduits from one point to another point though separate earthing cable is conncted from DB to Socket?

0 Answers  


difference b/w timer and counter

1 Answers  


why the transformer ratings in kva

8 Answers   NTPC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)