What are methods to avoid the inrush current at the time of
starting of power transformer ?
Answers were Sorted based on User's Feedback
We cannot avoid inrush current when any transformer is
switched on after a long period of shutdown. Only thing we
can do is minimising it by charging the transformer by the
lowest voltage (using tapp changers)and we can avoid
spurious tripping by inrush current by using only
transformer differential relays in which an inrush current
filter is used.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / vinothbabu.k
BRFORE STARTING ON THE TRANSFORMER WE SHOULD SWITH OFF ALL
THE OUTGOING FEEDER FROM THE DISTRIBUTED PANEL BOARD,THEN
ON THE TRANSFORMER WITHOUT CONNECTING ANY LOAD, THEN SWITH
ON THE FEEDER ONE BY ONE,R CONNECTED LOAD.THIS THE METHOD
TO AVOID THE INRUSH CURRENT FROM THE TRANSFORMER...
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / mukhesh
their is no chanses to avoid the magnetic inrush currents
in p t/f by wn inrush curens come the t/f will doing the
vibrations to avoid vibrations steel chains are fixced
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / makku
we can reduse inrush currrent by using winding having high reactance
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / priyan
You can reduce the second harmonic by using the DELTA
connection in the CT’s but I prefer to play with the
protection relay parameters, in this case it is better to
control the differential current, there is 2 slopes for the
differential zones, try to increase the slope N01 to get
passing the inrush current.
By filtering the 2 nd harmonics, refer to relay co
ordination and set the values
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / karthikeyan
Its recommended to install an CLR (Current Limiting Reactor)
befroe the Power Transformer to reduce the inrush current.
| Is This Answer Correct ? | 3 Yes | 7 No |
Answer / a.kossay
TO AVOID INRUSH CURRENT IN TRANSFORMER WE MUST USE A
VOLTAGE SENSE RELAY TO MONITOR THE VOLTAGE PEAK , SO WHEN
ITS VOLTAGE PEAK THE C.B CAN BE CLOSED AND INRUSH CURRENT
WILL BE LIMITED
| Is This Answer Correct ? | 1 Yes | 7 No |
orifice sizing how done, checking & selection
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
What is the life of MCCB
How Arc Produced in Circuit Breaker When the contacts of the circuit breaker open.
Which Transformer is commonly used for power distribution?
What is Goerges phenomina to start SYCHNOUSMOTOR?
when the control mechanism is present for an ammeter(1-10A) and 1A current is apllied what will be the reading of the meter?
what is phase to phase to phase to ground fault
why 30 ma elcb is used ?why cant 100 ma?
sir, my question is that if we start any three phase induction motor with star connection.will be current taken ? please send a formula.
What is breather? why we use it ?
I have a 5KVA UPS. Total load to be connected almost 3KW. Ordering a battery pack with capacity of 1920VAh. How long will the backup time be?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)