Answer / pankaj rajput
It will trip on over fluxing protection, if the protection
is installed.
It's not a wise situation to connect transformer to a lower
frequency with same voltage. The flux induced in core is
directly proportional to voltage & inversly proportional to
frequency. Hence the core will be over heated/over fluxed
and may get damage due to over heat.
The only remedy is reducing the voltage in same ratio.
| Is This Answer Correct ? | 31 Yes | 2 No |
Answer / ashokreddyreguri
flux is proportional to E\f or V\f
if the frequency is reduced the ratio V\f will increase so
flux will increase.so to maintain this flux magnetizing
current required will increase.this reduces the no load
power factor , so on load power factor is also reduced.
this also reduces o\p of transformer.so V/f ratio of t/f
must be maintained constant.
as 50% of frequency is applied to maintain constant V/f
input voltage applied must be 50%if rated voltage
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / eeaadil
60 Hz is expensive to generate and safer to operate than 50 Hz
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek goyal
Xmer is the static device which can produce the voltage in
secondary side WITHOUT CHANGING OF FREQUENCY. (Pl read xmer
principle. NO CHANGE REQUIRED.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sachin_pawaskar2001
Nothing............only you will get 25hz frequency at out
put.
| Is This Answer Correct ? | 0 Yes | 24 No |
How does "OUT OF STEP" relay ,for Synchronous motor protection, work?
What is mean by % impedance of transformer? detail explanations expected.
what is meant by lagging & leading current
What mean 150 amp hour write on battery.
We have .ht motor which is 60Hz.we run on 50Hz.so that it's speed reduce but we had one prob.that motor winding temp increase up to 135 deg.we want reduce this temp.what to do?we arrange ext.cooling fan but not much effect.we want reduce this temp. Inhouse without affecting much.cost. also don't want reWINDING OF MOTOR?
How RTCC panel is working and give single line diagram for RTCC with transformer?
how you taken aotitude test
Difference Between Isolator and Mcb
13 Answers VHB Medi Life Sciences,
WHAT IS SYNCHRONISING?
Is it possible we are step down 11 kv to 230v ?
1.why we are using metal oxide gapless block in lightning arrester,2.What is minimum and maximum rating of metal oxide blocks using in india
it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)