Answer / pankaj rajput
It will trip on over fluxing protection, if the protection
is installed.
It's not a wise situation to connect transformer to a lower
frequency with same voltage. The flux induced in core is
directly proportional to voltage & inversly proportional to
frequency. Hence the core will be over heated/over fluxed
and may get damage due to over heat.
The only remedy is reducing the voltage in same ratio.
| Is This Answer Correct ? | 31 Yes | 2 No |
Answer / ashokreddyreguri
flux is proportional to E\f or V\f
if the frequency is reduced the ratio V\f will increase so
flux will increase.so to maintain this flux magnetizing
current required will increase.this reduces the no load
power factor , so on load power factor is also reduced.
this also reduces o\p of transformer.so V/f ratio of t/f
must be maintained constant.
as 50% of frequency is applied to maintain constant V/f
input voltage applied must be 50%if rated voltage
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / eeaadil
60 Hz is expensive to generate and safer to operate than 50 Hz
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek goyal
Xmer is the static device which can produce the voltage in
secondary side WITHOUT CHANGING OF FREQUENCY. (Pl read xmer
principle. NO CHANGE REQUIRED.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sachin_pawaskar2001
Nothing............only you will get 25hz frequency at out
put.
| Is This Answer Correct ? | 0 Yes | 24 No |
What is earth fault?
they conducted technica for 1 hour..i also managed..they selected 5 boys and only one girl,myself got wait listed.whether they would call or not
why 120 devided with pole and speed multiplication to determine frequency
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases flux A does not alter B decreases C increases D none of above
Why in ESP Positive earthed
Why is transformer core is earthed
how can we calculate air compressure capacity
what is the function of statics switch in ups and tell me parts
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
Why derivative controller is not used in control systems?
hi!!! i have a question that how the thermal test in winding temprature test is taken can anyone explain me in detail??? i will b very thankful!!!!
whta is difference between contactor and breaker.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)