why does mA signal preferred for signal transmission?
Answers were Sorted based on User's Feedback
Answer / ashok bhatti
Current does not have any drop during transimission through
electrical wires however the voltage drops as the lengh of
elecrical wire used for transmission increases.
Thats why mA is preffered over mV etc.
Is This Answer Correct ? | 77 Yes | 4 No |
Answer / ibrahim s
mA Signal :-
1. Current measures remain same in any point of the signal
transmission line(no loss).
2. Less noise interference.
mV Signal:-
1. Voltage droup occurs(loss).
2. Noise interference is high.
So that mA signal is preferred over mV signal
Is This Answer Correct ? | 29 Yes | 3 No |
Answer / saravanan.m
MA IS PREFFERED THERE IS NO DROP IN CURRENT.SO ONLY MA
IS PREFFERED
Is This Answer Correct ? | 17 Yes | 5 No |
Answer / kush kumar
as we know voltage is noise sensitive ..so if transmission
is in the form of voltage then ll loose the original signal
nd at the reciever side ll not get accurate reading ,,but
in d form of current ..its not affected by noise
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / r santhosh kumar
most probably mA signal is preffered in signal transmission
because the voltage in the cable may be affected by the
sidewise power cables which are running with this cable
(in the same cable tray).
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / shan
mA is the ideal analog signal to be used because it has no
voltage drop. The same current will be recieved even in
100m transmission line.
Voltage signal is much accurate than mA but it is good only
for short range application because of its characteristics.
Prone to noise and voltage drop.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nikhil desai
NOISE REDUCTON AND NO CURRENT DROP FOR LONG TRANSMISSION LINE.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / daher
THE ELECTRICITY SPECIFIED AS HIGH VOLTAGE-MEDIUM VOLTAGE-
LOW V.-HIGH CURRENT -LOW CURRENT.mA is used in control
signals $communication ,computers......,
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / deepak
ma signal is preffered because current signal does not drop
during transmission through sigal cable as comapred to
volatage signal but sometimes it gets affected by the stray
pickups that can e eliminated by connecting the shielding
at one end.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / vipul joshi mfl
The voltage will drop at the length of the cable but in the
case of mA the current will not drop at the receiver end so
we preferred the current as a signal transmission and for
4-20 mA it is preferred cause the 4 mA is a signal we use as
a zero value if we use 0-12 or 0-20 mA then if any break in
cable was there, we cannot judge.
Is This Answer Correct ? | 2 Yes | 0 No |
why r using 250 resistances
What are the uses of orifice plates?
where are following valves are applicable to install. can any valve be installed any line. globe valve butterfly valve boll valve gate valve
why we connect digital multimeter in series for dc current measurement and parallel for dc voltage measurement.
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
Im having problems with interfase betwen SPI v7.0 and SPPID v5.05. Previous versions of Intools shoul be fixed with SPPIDproj.ocx file. It was necessary to replace this file with one that allows the connection between different versions of SPPID. It is necessary in the current version to do the same?Thanks
IF I WANT TO BUY A THERMOCOUPLE THEN WITCH PARAMETER I LOOK
dear sir we have insatlled positioner model no.sipart PS2 make Siemens at our control valves . now problem is if we want to increase the response of valve opening speedy /fast. what parameters do we change for positioner ? any idea. please guide us.
Somebody ask me how many size of control valve what is mean of control valve size?
What kind of feedback is used in DP cells.
re i got gre score of 950,and toefl of 69 is this score sufficient actually my husband is presently in US i need to go please help me
meaning of SMART