Range 8 Kg/cm2, alarm to be set at 2Kg/cm2, at wat pressure
reciever switch to be calibrated? justify the ans?
Answers were Sorted based on User's Feedback
Answer / shan
we are to calibrate at the pressure switch. Pressure switch
is the pressure reciever.we have to set the pressure switch
at 2Kg/cm2. If pressure reaches 2Kg/cm2,it will alarm.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / mithilesh kumar
1st pr. switch is combination of NO,NC,COMMON.OK.
for setting alarm at 2kg/cm2.
it calibrate with DEAD WEIGHT TESTER at 2kg/cm2.during
calibration NC becomes NO and NO become NC.it check with
multimeter in continuity mode.ok.
if it's done then your calibration is ok.
then you can use as per requirement.
any comment.
most welcome
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / welcome4ujd
if range is 0 to 8 kg/cm2, an d alarm needed is 2 kg/cm2.
that is 25 percent of range, set the alarm at 6 psi of a 3
to 15 psi out put.
and if it is a flow transmitter of some range,say 0 to
1000 mmwc and alarm at 250 mm
then 25 % of flow in transmitter will give square root 25
devided by 10 tht is 50 percent in the control room , so
you have to set 50percent in the receiver switch that is 9
psi for a 3 to 15 psi out put.for basic flow transmitter
to find out square rooting from field to ccr
just square root the input percentage and devide by 10
to find the field input from control room signal
devide the ccr signal percentage by 10 and square it.
| Is This Answer Correct ? | 2 Yes | 7 No |
How many ohms are required for proper earthing?
what is sequence table in DCS . make a logic in sequence table for tripping of ID fan in Boiler(in YOKOGAWA CS 3000 DCS).
HI friends.I am Surya a BTech in Electronics and Instrumentation Engineering.I am going to appear Relince Industries Ltd all India writen test very soon. so plz help me by sendind the probable questions about my subject.My mail ID is surya.barik@gmail.com.
why we use -ve voltage in vibration monitoring system.generally we use 4 to 20 mA as output of instrument then why we use voltage in vibration
i want to measure temp of hot sand(welding flux) in closed chamber(around 150 deg C).Which is better thermocouple or thermometer?
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
Can anybody explain about wellhead control system.
Which wiring connection is preferred in motor for industrial use?
what is bevel? why bevel required in orifice plate?
Draw a great bridge circuit.
If the on Of the DO module is off in the System cabinet, then what is the Procedure to check weather the Module is working or not.
I am working in a process industry, in that there are several sections devided in the SCADA screens and individual sections may START independently. But sometimes i am facing problem i.e, if section 2 Stopped by the operator immediately Section 1 or Section 3 or Section 4 is getting stopped can you expain the reason behind this?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)