Range 8 Kg/cm2, alarm to be set at 2Kg/cm2, at wat pressure
reciever switch to be calibrated? justify the ans?
Answers were Sorted based on User's Feedback
Answer / shan
we are to calibrate at the pressure switch. Pressure switch
is the pressure reciever.we have to set the pressure switch
at 2Kg/cm2. If pressure reaches 2Kg/cm2,it will alarm.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / mithilesh kumar
1st pr. switch is combination of NO,NC,COMMON.OK.
for setting alarm at 2kg/cm2.
it calibrate with DEAD WEIGHT TESTER at 2kg/cm2.during
calibration NC becomes NO and NO become NC.it check with
multimeter in continuity mode.ok.
if it's done then your calibration is ok.
then you can use as per requirement.
any comment.
most welcome
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / welcome4ujd
if range is 0 to 8 kg/cm2, an d alarm needed is 2 kg/cm2.
that is 25 percent of range, set the alarm at 6 psi of a 3
to 15 psi out put.
and if it is a flow transmitter of some range,say 0 to
1000 mmwc and alarm at 250 mm
then 25 % of flow in transmitter will give square root 25
devided by 10 tht is 50 percent in the control room , so
you have to set 50percent in the receiver switch that is 9
psi for a 3 to 15 psi out put.for basic flow transmitter
to find out square rooting from field to ccr
just square root the input percentage and devide by 10
to find the field input from control room signal
devide the ccr signal percentage by 10 and square it.
| Is This Answer Correct ? | 2 Yes | 7 No |
Sir , i have completed my M.Sc In Instrumentation and presently working in Maintenance department 3 yrs Exp , is there is any possible for work in offshore ..
As you are fresher in Instrumentation & control engineer.Then why should I select you?
What is impulse line size
what is commisioning procedure,2)what is is the main work in commisioning in the field tx to dcs, plz send me detail
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
admittance level sensor meaning?
in split range control system we are using two control valves,but we have only one positioner and one feed back link.so how we use this one feed back link for two control valves?
what is differences between singal acting and double action valve
1 Answers Carlo Gavazzi, Welspun,
Where do we consider the pressure in mbar & where do we consider the pressure in bar & why is it so ?
2 Answers BOC, Jindal Steel and Power,
What is input and output of plc & dcs
where proximity sensor installed on tank in loading arm application
I am working in a process industry, in that there are several sections devided in the SCADA screens and individual sections may START independently. But sometimes i am facing problem i.e, if section 2 Stopped by the operator immediately Section 1 or Section 3 or Section 4 is getting stopped can you expain the reason behind this?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)