Can I put my meter across an RTD to check it safely witout
tripping the equipment when it is connected to an
monitoring device eg.RTD module or IQ 1000
Answer / s.k.bakshi
Yes you can do it.
1. force the analog input with such a value so that it is
beyond the tripping value.
2. Then open the leads and check the resistance of the rtd
in order to check wheather the rtd is faulty or not.
Is This Answer Correct ? | 3 Yes | 0 No |
how to check earthing,what is minum ohms for proper earthing
please give me the syllabus and sample questions if possible for Instrumentation for Vizag Steel plant MT (Trainee) 2009 exam
1 Answers Pedvak, Steel Plant, Vizag Steel,
how do i calibrate mmwc pressure guage with out calibrator.if any? pls give me the ans.
what is seebeck effect?
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?
what are the values of fuel flow rate in various places in boiler.
Which standard of hazardous area classification used in India?
i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....
what is the formula for calculating milliampere at different pressure points for eg 4-20 ma = 3-15 psi but if i have to check the ma at 4.6 ma?
How do understand by hart protocol?
4 Answers BW Instrumentation Electrical,
what are the levels of automation?