How to make vector group test of transformer?
Answers were Sorted based on User's Feedback
vector group testing: Assume that the terminals of the
primary windings are denoted as A, B, C in counter clock
wise direction and for secondary winding as a, b, c also in
counter clockwise direction. short circuit the terminals A
and a, and apply LT supply to the three terminals of HV
(Aa, B, C)
For Dy1 transformer: VbB = VcB and VbC grater than VcC.
For Dy11 transformer: VbC = VCc and VBb less than VcB.
For Yy0 transformer: VBb = VCc and VbC = VBc.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / debasrit das
i need some more answers about vector group testing
Is This Answer Correct ? | 0 Yes | 0 No |
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?
What is difference between safe PLC and normal PLC
what is the function of compressor?
Why carbon brushes are used in motors?
what the function breaker failure scheme, how is it operated
How can we calculate the Rating of DG Set for a 4 kw motor?
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
In Siemens S7-300 PLC, what is funtion and funtion block ? What is the difference between them ? When to use function and when to use function block
why moisture formation found in XLPE Armoured cable outer sheath
why we use separate earthing for two seprate machine??
why the conservater tank alwes made upper side of transformer???
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<