How to make vector group test of transformer?
Answers were Sorted based on User's Feedback
vector group testing: Assume that the terminals of the
primary windings are denoted as A, B, C in counter clock
wise direction and for secondary winding as a, b, c also in
counter clockwise direction. short circuit the terminals A
and a, and apply LT supply to the three terminals of HV
(Aa, B, C)
For Dy1 transformer: VbB = VcB and VbC grater than VcC.
For Dy11 transformer: VbC = VCc and VBb less than VcB.
For Yy0 transformer: VBb = VCc and VbC = VBc.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / debasrit das
i need some more answers about vector group testing
Is This Answer Correct ? | 0 Yes | 0 No |
what is the working principle of UPS?
how to calculate neutrel current
Dear Friends, I have a 500KVA transformer supplying whole factory having 3 phase and single phase mixed loads. Power room has ammeters connected via CTs for individual phase. Now I know that readings shown on meter for each phase say R,Y and B are line currents. But when I want to know the total on transformer do I need to add the currents of all three phases readings shown on meter or value for anyone phase will give me the correct power load on transformer for that point of time. 2. If ammeter shows unbalanced readings for R,Y, B phases say 150, 250 and 300 respectively so can I assume that 150A i.e average of 3 will be the 3phase load currents and remaining will be 1phase currents. Please clarify my doubt.
The rating of Transformer are 11KV, 22KV, 33KV instead of 10KV, 20KV & 30KV?
we have one 75kw motor 380 volt 3ph amp134 please advise which size of cable required
What do you mean by passive circuit elements and why these are called passive?
what is the reason the main breaker is trip during the motor is running? (some time the breaker is not trip)
we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when we are charging the same cable with 11 kv supply why the VCB 11 kv gets tripped can anybody define the possible cause of fault ?
How should i design a 1ph & 3 ph transformer. Kindly let meknow all steps and formulaes related to design from scratch.
What is meant by soft starter used in motors?
why dc supply is given for excitation of ac alternator?how dc can produce flux?
for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single phase.why