what is the technical diffrences of mccb and acb
Answers were Sorted based on User's Feedback
Answer / pks
MCCB is Moulded Case Circuit Breaker & ACB is Air Circuit
Breaker...
Use of these both CBs depends on requirment of Current
ratings. If Much higer is the current, ACB will be used &
MCCBs may be used for lower values of currents.
| Is This Answer Correct ? | 45 Yes | 9 No |
Answer / krishanu bhattacharya
Generally speaking, ACB are used as main incomer protection,
that means just after the transformer as the highest short
circuit current would be available just after the
transformer whereas MCCB are used as protection in outgoing
feeders where current rating & SC Breaking capacity needed
is a bit less than ACB. Though now a days MCCB and ACB both
can break a 100kA fault, but the main difference is:
ACB is category A breaker whereas MCCB is category B. that
means ACB can withstand the high SC current for a few
seconds so that the whole system will not trip just for a
small fault but in case of MCCB there is no withstand
capacity, if there is that too for ver smaal time in ms. So,
physical dimension of ACB are moere than MCCB. Thanks
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / sunthosh080
All the above answers are correct and little more to add
from my side.
usually these breakers are used for short circuit
protection to a valid value.
The max. KA in MCCB is 50 KA and in ACB it is 100KA. So the
selection also depends on the short circuit level to be
protected.
Now a days all the breakers are microprocessor based
protections with all parameters.
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / jeet
i also want add little facts like you for BCH
ACB - available above 800 A in BCH make
MCCB - available from 10 A to 4000 in BCH make
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / sandip
In addition to that ,In ACB MAINTENANCE IS POSSIBLE .iN
MCCB IT IS NOT.LIFE OF ACB IS MORE AS COMPARE TO ACB.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / dudeblore
MCCB- moulded case circuit breaker
ACB - Air circuit breaker
Normally ACBs are being used in high current systems where
as MCCB with current less than 1500A. The main difference
depends on the arc quenching meddium. In ACB air is used as
arc quenching medium and MCCB will be operated like other
breakers like MCBs, etc...
| Is This Answer Correct ? | 18 Yes | 21 No |
Answer / naren
i want add little facts
ACB - available above 800 A in L&T make
MCCB - available from 10 A to 1400 in L&T make
| Is This Answer Correct ? | 5 Yes | 8 No |
Answer / ritesh
All answers are correct but if any body want to be use as a
door protection or overvoltage protection.MCCB give both
protection.
| Is This Answer Correct ? | 2 Yes | 15 No |
Answer / amit sonmale
MCCB can be used in the saftey of machines for LT side with
higher Amps ratings i.e.. upto 250Amps.
But ACB and VCB are used in the HT side only.
But all the three are used for short circuit trippin and
fault tripping.
ACB and VCB are highly sensitive and based on various
factors like Milliamps setting,Short circuit time etc..
| Is This Answer Correct ? | 6 Yes | 19 No |
what main difference betwenn invetter & ups & major difference
In ac which gas will be use?
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
What is a soft start?
What is working principle of ACB and VCB?
differentiate between one way two gang switch & two way one gang switch, used in designing the loads of building.
why active power is called as real power or working component.What is the exact function of active, reactive & apperent power.
What is meant by CFL & PL lamps
in 31.5 mva power transformer how to set of wti and oti?
What are the advantages & disadvantages of a group electrive drive?
WHAT HAPPENING TO TRANSFORMER???? i have the step down transformer rating 230/12v, power rating something.,,, ok. suppose iam giving 12v to secondary side,what will happen on primary side.,,,
What differance between Circuit brekar and Isolater?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)