WHAT IS THE Differance b/w on/off & pid control valve?
Answers were Sorted based on User's Feedback
Answer / indranil mukherjee
ON/OFF CONTROL VALVE WORKING IN TWO MODE EITHER ON OR OFF.
BUT PID CONTROL VALVE IS TOTALLY CONTROLABLE.MEAN ITS
OPENING OR CLOSING SCALE IS BETWEEN 0 TO 100% OR VICE-VERSA.
Is This Answer Correct ? | 72 Yes | 8 No |
Answer / ytd
ON/OFF CONTROL VALVE WORKING IN TWO MODE EITHER ON OR OFF.
In ON off control process has shoot up and down. This
process is not suitable for critical processes.
E.G.controlled heating / cooling for Annealing cycle.
PID control generally used in close loop process where
feedback of output is used to correct the input depend upon
the desired process.
S(o/p)= S(i/p)+/-(S(correction).
From this simple equation o/p signal is corrected but
depending upon the responce of the process `Diffential
gain' or integral gain is introduced and this simple
equation is modified.
Depending upon the process performance responce time ang
gain values are to be programmed in the PID controller.
Then PID controller follows the equation to make process
more controlled.
Is This Answer Correct ? | 51 Yes | 8 No |
Answer / m.v.ramesh
Most ofthe answers are right, but the basic question is a
bit diverting in to other direction.
Question has to be like this.
What is the difference between On-Off control valve and
regulatory control valve.
Dont call as PID control valve. offcource regulatory
control valve is controlled by p or I or PI or Pd or PID
controlling modes.
Regulatory control valves can be operated by hand wheel
also with out PID controllers, some applications with
manual pneumatic regulators.
rest all answers are ok. simply on-off valves have 2
positions and regulatory valves can have n number of
positions in its range. selection of these are process /
design dependent.
Is This Answer Correct ? | 26 Yes | 0 No |
Answer / kavi
Both are used to control a process. The on/off valves are
actuated by simple digital signal ( may contain voltage of
24 vdc/ac to 220vac) from an on-off controller or from a
controller whose output is of "on-off PID". In the first
one when the process exceeds a set value ( increase or
decrease) the digital output goes to valve to operate a
solenoid whose air supply opens or closes the valve ( a
full close or open condition). If the controller is having
an on-off PID the digital signal going to the valve is the
output of PID block of the controller which is in the form
of pulse width modulated one. In this also the valve will
have only two states like fullopen or full-close. In the
so called PID valve, the valve can have any postion of
opening basing on the analog signal received from the
controller. We can say that the valve opens or closes
proportional to the analog signal from the controller. In
this the controller tuning ( setting the values of P, I D )
has to be done by the process operator or the concern
instrument engineer/technician.
Is This Answer Correct ? | 18 Yes | 1 No |
Answer / surendra gupta
on/off controller are simple type controller, they simply
on or off the o/p. where as pid controller, two additional
functions are added that are integral and derivatives.
2) on/off controller are not used for the closed ckt where
as pid controller are used for closed ckt.
Is This Answer Correct ? | 19 Yes | 4 No |
Answer / sabitha reddy
THE BASIC CONTROL VALVE SET UP WIL BE DESIGNED IN ORDER TO
UNDERSTAND THE CONTROL VALVE OPERATION AND IT'S FLOW
CHARACTERSISTICS..INHERENT FLOW CHARACTERISTICS CONSISTS OF
PNEUMATIC CONTROL VALVES OF LINEAR,EQUAL PERCENTAGE,QUICK
OPENING(ON/OFF)..
COMING TO THE DIFFERENCES BETWEEN CONTROLLERS IS--
ON/OFF IS DISCONTINUOUS WHERE AS PID IS CONTINUOUS ONE
(WHICH ATTEMPTS TO CORRECT THE ERROR BETWEEN MEASURED
PROCESS VARIABLE AND DESIRED SET POINT )AND IT'S OUTPUT
CHANGES SMOOTHLY...
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / jobby c johnson
on /off controller is a discrete state controller
whereas PID is an continous state controller
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / amit mukherjee
In on-off controlling the o/p of controller gets on as it goes
below setpoint and vice versa when it goes up.But in PID control the controller tries to open final control element and
analyse error(e=sp-pv) and act according to their to their action.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / bell
on/off will make full open or full closed position of the
valve,but pid will give percentage of valve open/close
according to the controller output.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / sudipta,iter
on/off control is not closed loop where pid is closed loop
system.
Is This Answer Correct ? | 8 Yes | 15 No |
how to calibrate electro pneumatic positioner 8013 mil controls ltd ?gsr
diff c and c++
when a magnet is heated?
What is mean by ATEX?
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
How to Calibrate Coriolis Flow transmitter in field
what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC
1 Answers Bharat Biotech, TATA,
pressure gauge measure static pressure or dynamic pressure?
I want to measure bidirectional steam flow? Kindly suggest me a suitable flow meter. steam is superheated at 41kg/cm2, 350°C
what is the Difference Between Domain and Station?
why we use 4-20 mA for calibration of the instruments.why we cant use 0-20 mA?
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?