Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calibrate DP transmitter by using HART communicator ?



How to calibrate DP transmitter by using HART communicator ?..

Answer / sunilkumar tailor

Step:
*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.




*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
WARNING – If the process is hazardous, please unsure proper flushing is done to remove the entire hazard.
*Open vent valve at drip ring and open plug at the top of the drip ring (if available) to release the process pressure
*Clean the liquid inside the drip ring and put back the plug for high side only (if available).
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*In this condition both capillary flange will be atm pressure at difference high
* Multimeter should show 4mA and PV at HART communicator should shows 0 (LRV)
*If not, do zero adjustment at transmitter using HART Communicator
*Connect pressure calibrator to high side flange (drip ring)
*Apply pressure depend data sheet span (URV)
*Multimeter should show 20mA and PV at HART communicator should shows same with URV
*If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.
















Note: 




Capillary flange at same elevation
Example calculation:
Transmitter range = 0-2 kg/cm2
LRV = 0 kg/cm2
URV = 2 kg/cm2.

Is This Answer Correct ?    5 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Can we get the outpot in c without using getch fiction? Answer is yes but output will stay on display 4 only few second.... But can we get output without using getch and also output will hold on the display...?

1 Answers  


WHAT IS ANNUBAR?

7 Answers  


Which type of pressure can be measured by primary elements?

0 Answers  


Im having problems with interfase betwen SPI v7.0 and SPPID v5.05. Previous versions of Intools shoul be fixed with SPPIDproj.ocx file. It was necessary to replace this file with one that allows the connection between different versions of SPPID. It is necessary in the current version to do the same?Thanks

0 Answers  


i have one absolute pressure transmitter for the range is -400mmhg to 400mmhg. If i do the zero trim at atmosphere the transmitter should be give 4ma or 12ma? which one is correct?

2 Answers  


What properties or parameters to be taken into consideration for protection while selection of Dcs controller.

1 Answers   JPL,


without color coding, without nameplate, without multimeter how can you find the type of thermocouple???

1 Answers   Sabic,


How you calibrate absolute pressure with the calibration range of 0 to 1000 0C Absolute. Please explain the procedure for calibration.

0 Answers   Petro Rabigh,


Where we cant instal mass flow meter.

1 Answers  


what are the three main programming languages in plc

12 Answers  


What is seeback effect?

3 Answers  


what is the approximate cost of U tube manometer having range 1000mmwc to 1000mmwc?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)