Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calibrate DP transmitter by using HART communicator ?



How to calibrate DP transmitter by using HART communicator ?..

Answer / sunilkumar tailor

Step:
*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.




*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
WARNING – If the process is hazardous, please unsure proper flushing is done to remove the entire hazard.
*Open vent valve at drip ring and open plug at the top of the drip ring (if available) to release the process pressure
*Clean the liquid inside the drip ring and put back the plug for high side only (if available).
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*In this condition both capillary flange will be atm pressure at difference high
* Multimeter should show 4mA and PV at HART communicator should shows 0 (LRV)
*If not, do zero adjustment at transmitter using HART Communicator
*Connect pressure calibrator to high side flange (drip ring)
*Apply pressure depend data sheet span (URV)
*Multimeter should show 20mA and PV at HART communicator should shows same with URV
*If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.
















Note: 




Capillary flange at same elevation
Example calculation:
Transmitter range = 0-2 kg/cm2
LRV = 0 kg/cm2
URV = 2 kg/cm2.

Is This Answer Correct ?    5 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

why we are using analytical instrument in plant ?

1 Answers  


Identification of control valve parts.

0 Answers   CCIE, Oil and Gas Jobs,


what is meaning of software redundency and hardware redundency?

2 Answers   Honeywell,


dear friends, i have seen flow as the selection critriea in presure guage (bourdon tube) and i would like to know what is the relation between flow and performance of pressure guage other parameters i found in the data sheet are pressure max. 1ksc temperature max. - 50 deg c line size - 80NB operating range - 1ksc pr. guage range - 0-2 ksc thank u,

0 Answers  


how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp side?

5 Answers  


Please send me the sample question of Instrumentation of hpcl/iocl exam. my mail id hihi_kiholo@rediffmail.com

0 Answers  


flow transmitter formula?

0 Answers   BEMCO, Siemens, Yokogawa,


PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..

3 Answers  


What happen if we install my pressure transmitter below the elevation of pipe in natural gas service?

0 Answers  


How to change dcs card in online. (Dsc is maxdna)

3 Answers  


IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?

0 Answers  


1. What means HART communicator / where it is used / how to use it? 2. Types of Thermocouples and its temperature ranges / output of thermocouple? 3. Types of RTDs and its temperature ranges / output of RTD? 4. Idea about Temperature Transmitters? 5. Difference between Analog and Digital signals? 6. Difference between “2 wire” and “4 wire” system / instruments? 7. Difference between “Potential” and “Potential free” contact? 8. Types of flow meters / transmitters? 9. Types of level transmitters? 10. Difference between “Power/Control” cable and “Instrument” cable? 11. What means “shield” and “screen” in cables / how it is useful? 12. Draw a schematic of closed loop circuit of flow / level / pressure / temperature? 13. Idea about calibration of Control valve / positioned / I/P? 14. How to bypass a digital/analog signal in PLC/DCS by hardwire and software?

6 Answers   JSL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)