How to calibrate DP transmitter by using HART communicator ?
Answer / sunilkumar tailor
Step:
*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.
*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
WARNING – If the process is hazardous, please unsure proper flushing is done to remove the entire hazard.
*Open vent valve at drip ring and open plug at the top of the drip ring (if available) to release the process pressure
*Clean the liquid inside the drip ring and put back the plug for high side only (if available).
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*In this condition both capillary flange will be atm pressure at difference high
* Multimeter should show 4mA and PV at HART communicator should shows 0 (LRV)
*If not, do zero adjustment at transmitter using HART Communicator
*Connect pressure calibrator to high side flange (drip ring)
*Apply pressure depend data sheet span (URV)
*Multimeter should show 20mA and PV at HART communicator should shows same with URV
*If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.
Note:
Capillary flange at same elevation
Example calculation:
Transmitter range = 0-2 kg/cm2
LRV = 0 kg/cm2
URV = 2 kg/cm2.
| Is This Answer Correct ? | 5 Yes | 0 No |
hay friends, i am in trouble to understand PID controller. several times i have study but it is not clear to me have you a simple way to understand.
what does mean by analog output trim and where this one used for?
Hi Friends i am going to write BARC written test by this month 20th (20-5-2008). So please if any body knows the details about this or having previous question papers pls mail me to kkumarei@gmail.com. For Suggestions give one message to 9962122264
Operational amplifiers
what are the three main programming languages in plc
Describe a time when you anticipated potential problems and developed preventive measures.
Yokogawa dcs nodes advantages?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
HOW DPT WORKS?
Could anybody pls give ans of boiler 3 element control system?
How to derive IO Count (AI, AO, DI and DO ) from a Field instrument (FI) Bill of Quantities (BOQ) given by client.
What is the cv of a control valve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)