Answer / amarnath
CBCT is Core Balancing Current Transformer and ELR is Earth
Leakage Relay...
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / j. nagarajan
It should not be called as CBCT ELR. Actually this is an
Earth Leakage Relay sensing the leakage current through a CT
provided at Cable end called CBCT, to protect the incomer.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / subhash sahu
ELR Earth Leakage Relays along with CBCT are used to detect
leakage current in the earhing. If the earthing is not
proper a small amount of current will appear (in the order
of mA). ELR will continuously monitor the leakage current
if it exceeds the set threshold an output electromechanical
relay (which is inside the ELR) will operate. The output
relay contact can be connected to circuit breakers /
contactor to isolate power supply or alarms.
CBCT Core Balance Current Transformers these will come in
different sizes. the core material will be either nickel or
alloy of nickel, copper wire will be wounded on the core
and properly insulated. The 3-phase line along with neutral
are passed in this core and secondary is connected to ELR.
Idealy the leakage current should be zero if any earth
leakage happen the leakage current will appear at CBCT
secondary it will be detected by ELR.
| Is This Answer Correct ? | 0 Yes | 0 No |
why middle phase should used for earth fault and other phases used for over current in overcurrent and earth fault relay?
why the single phse machine can not run by the three phase supply.
what is a vector protection in transformer
What are reasond for high wattage in single phase induction motors
What is the main feature of v/f control?
it is used to measure the potial difference between two point?
how to calculate AH of a battery?
what is the avr
6 Answers ArcelorMittal, Heidelberge Cement,
What is the criteria for selecting the voltage classes of an AC Induction Motor.The KW rating above/below which ht/lt selection is made may be provided in details.
Dir sir we have 750 kva Caterpillar dg set we are fas on different problem we start dg set ofter 1 mint apply load around 500a dg was run one or 3 mint after 3 mints dg was shutdown automatic how to face tis problem
if acapacitor connected to power supply will it cosume power& will it going to get recorded in energy meter
What are the advantages of star-delta starter with induction motor?
7 Answers Merchant Navy, Naval Academy, Samundra Institute of Maritime Studies, YMCA,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)