I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
The initial in-rush current is about 3-4 times the normal current when there is stabilizer as it consists of a transformer . If you keep the switch of the MCB pressed with your finger for a short time while switching on the AC ,the MCB may not trip. You can go in for a 30A MCB
Is This Answer Correct ? | 0 Yes | 3 No |
what is the need of reactor in between the transmission line?..like powergrid like that..
hi i have a 400kva transformer i want to know the test i can use to check on it thx
how the B-H loop obtain under the static condition
why are transformers rated in KVA and not in KW
Which rccb 30ma,100ma,300ma sensitivity should be used in domestic line and what is difference, advantage and disadvantage of all three
What's is the difference between IVT and CVT?
The screw thread commonly used for transmission of motion is one of the following types of threads
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
How to connect the earthing in aircraft?
What kind of preventive maintenance are there for AC induction motor?
Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KVA T/F in our site, can you help me that how many maintenance tests can be conducted and what are the procedures included for the tests can you share yours answers and also give any web address to get more information on this
My switchgear busbar is rated at 2000A and just imagine the actual load on busbar is 1000A. From that busbar there are 10 outgoing feeders. Now the question is will the load be 1000A on each outgoing feeder or 100A per outgoing feeder. 2nd thing how do i calculate the load on individual feeder. Thanks for your time. Please provide some clarification on this issue.