Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is Rough Balance Busbar Protection



What is Rough Balance Busbar Protection..

Answer / joe 90

The rough-balance scheme shall be driven from three phase CTs fitted on the LV side of the transformer incomer circuit and on the bus section which shall be connected in parallel into rough-balance zone protection relays fitted on the bus section panel. These relays shall have a fast acting highset definite time overcurrent element and IDMT overcurrent and earth fault elements. The relays shall be set to be stable under normal and through fault conditions and to operate for an in-zone busbar fault where the fault is fed from each side (incomer and bus section) to summate at the relay. Note that for correct operation of this scheme the feeder circuits must be connected in-zone i.e. between the incomer and bus section.
A trip output from the rough-balance zone relay shall operate into the bus section trip coil and a ‘trip repeat’ output fed into the protection relays for the incomer and all feeders connected on to the faulted busbar zone via a busbar zone trip buswire. On receipt of the busbar zone trip input the incomer and feeder relays will initiate a trip output to trip their respective circuit breakers.
For a feeder fault both the feeder and bus zone protection may pickup. A means must
therefore be provided to discriminate between a feeder and busbar fault so that the bus zone protection does not have to wait to give the feeder protection time to operate in instances where the fault is on the feeder. This is done by a block signal from the feeder protection start which holds off the high set definite time bus zone protection giving the feeder protection time to operate to clear the fault. If the fault is on the busbar the feeder protection will not pick up, no block is present and the bus zone protection can operate almost instantaneously.
Where the feeder protection fails to clear a fault (e.g. circuit stuck breaker), the bus zone
protection IDMT elements will operate to trip the bus section and set the bus zone trip output high. The feeder protection start must be set low on completion of the feeder protection operation to remove any block to the bus zone protection to allow for stuck breaker situations.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what are the problems faiced at dg comissiong

0 Answers   Aster Teleservices,


explain LED lamps?

1 Answers  


What is conventional thermal current (Ith)

0 Answers   Alstom, HPL,


why do we need transformers?

12 Answers  


how is the testing of an REF relay? what are the test REF circuit having?

0 Answers   Siemens,


how many types of ratings are there of transformer

5 Answers   Met Trade,


Define non-touching loop.

0 Answers  


I am working as a software engineer for the past 4 years. I am interested to do M.tech in premier inst. like IIT, IIIT, NIT,... I am preparing for the GATE exam for the past 2 years. Can anyone tell me how about the placement in IIT's for m.tech in (microelectronics and vlsi or electronics related discipline). Some of them are telling like placement is very rare for m.tech electronics. Also the placement details in IIT websites are not true. Is that so ? can any one help us regarding this.

1 Answers  


why substation rating interms of 11 multiples???like 11kv/33kv iis there any special reason???

5 Answers  


what is earth resistance? how to measured? and give values at power station and mcc area?

0 Answers   Essar,


How to determine the short circuit current for breakers and VCB.

1 Answers   Sabic,


What are the different methods of improving power factor,especially in Wind Sector

2 Answers   Suzlon,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)