Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is Rough Balance Busbar Protection



What is Rough Balance Busbar Protection..

Answer / joe 90

The rough-balance scheme shall be driven from three phase CTs fitted on the LV side of the transformer incomer circuit and on the bus section which shall be connected in parallel into rough-balance zone protection relays fitted on the bus section panel. These relays shall have a fast acting highset definite time overcurrent element and IDMT overcurrent and earth fault elements. The relays shall be set to be stable under normal and through fault conditions and to operate for an in-zone busbar fault where the fault is fed from each side (incomer and bus section) to summate at the relay. Note that for correct operation of this scheme the feeder circuits must be connected in-zone i.e. between the incomer and bus section.
A trip output from the rough-balance zone relay shall operate into the bus section trip coil and a ‘trip repeat’ output fed into the protection relays for the incomer and all feeders connected on to the faulted busbar zone via a busbar zone trip buswire. On receipt of the busbar zone trip input the incomer and feeder relays will initiate a trip output to trip their respective circuit breakers.
For a feeder fault both the feeder and bus zone protection may pickup. A means must
therefore be provided to discriminate between a feeder and busbar fault so that the bus zone protection does not have to wait to give the feeder protection time to operate in instances where the fault is on the feeder. This is done by a block signal from the feeder protection start which holds off the high set definite time bus zone protection giving the feeder protection time to operate to clear the fault. If the fault is on the busbar the feeder protection will not pick up, no block is present and the bus zone protection can operate almost instantaneously.
Where the feeder protection fails to clear a fault (e.g. circuit stuck breaker), the bus zone
protection IDMT elements will operate to trip the bus section and set the bus zone trip output high. The feeder protection start must be set low on completion of the feeder protection operation to remove any block to the bus zone protection to allow for stuck breaker situations.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between RMS & TRUE RMS VOLTAGE

0 Answers   IIT,


What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.

0 Answers  


What is the make of breakers, transformers, generators? What are their capacities and ratings?

4 Answers   Bharat Bijlee, GHPPL, Tata Motors,


what is the transformer

6 Answers  


how much watts the computer will takes

2 Answers  


why DG sets power factor is 0.8 lagging.

1 Answers   Cummins,


1 Kva = How many KW

3 Answers   Reliance,


Im designing APFCR Panel for 600 KVAR.I need to calculate the full current so that i can choose the capacity of isolator/Breaker.Kindly suggest with formula.

1 Answers  


how to calculate the step resistance for slipring induction motor,how you deside the no of step for that?

0 Answers   ABB, Visa,


can we produce cosine wave instead of sine wave? will it usefull?

4 Answers   BARC,


What is nyquist contour?

0 Answers  


In the case of petrochemical area AC drive & AC motor is used where the speed variation is required. Why they are not Using DC drive & DC motors in such areas?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)