how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?
Answers were Sorted based on User's Feedback
Answer / prashant soni
HT Cable size dependson fault level to be withstood and its duration..
If you take XLPE, HT Cable of ALU conductor,
condiering 350MVA for 1 sec *(18.37kA), min. C/A will be found out by Area(A) = (Short ckt current (kA)*Square root of Time)/k
k is constant = 0.094 for XLPE ALu conductor.
This will give you min. size required for HT system (11/22/33/6.6/3.3kV)
Choose nearest standard higher size for HT Cable..
primary 3*240 sqmm AL cable
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ahmed
how many cable shoul be connected for 2000kva transformer of 11kv.
primary 3*240 sqmm AL cable
Secondry 4*630 sqmm AL / single phase (L1,L2,L3 & L4)
(u1,u2,u3 & u4) R-Phase
(v1,v2,v3 & v4) Y-Phase
(w1,w2,w3 & w4) B-Phase
(N1,N2,N3 & N4) Neutral
| Is This Answer Correct ? | 2 Yes | 2 No |
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase), before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
How to improve insulation resistance of Motor
Dear all, i completed M.E(Power Electronics & Drives) 2011 passed out having 78% so i need job in core side but i don't know how can i receive the calls from electrical companies and i uploaded my CV in naukri, times jobs etc.. In that iam not recieved any mails from good companies so give me best procedure plzzzzzzzzzzzzzzzzzzzzzzzz..... Thanks, K.Linga Reddy Email-id:-lingareddykmthm@gmail.com Ph no:-08015402078
where used impendence relay?
Dear all i am kumaravel. now in chennai. my work is control and relay panel auto cad designing.up to 11kv to 400kv then question is i am improving my knowledge. i want some books name and auther are available for this C&R panel related. plese any one help me
What happens if we give ac supply to dc shunt and series motors individually
HOW DEFINE THE IP FOR ELECTRICAL EQUIPMENT AND WHAT IS THE IP OF PANELS USING IN HAZARDOUS AREA ?
Why the Motor takes High Current in Starting time?
What is the mechanism of WTI
Can you explain about Restricited earth fault protection scheme
WHAT IS DIFFERENCE BETWEEN PHASE CONVERTER AND VFD
Slow acting fuses are most often used for which application a) Lighting circuit b) heating circuit c) Motor D) Radar circuit
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)