1.What is wind span ,wight span and normal span, and what is the difference for 132kv transmission .
*The wind span is that on which the wind is assumed to act transversely on the conductors and is taken as half the sum of the two spans, adjacent to the support.In order to take full advantage of towers located on elevated ground, it is usual to allow a wind span of 10 to 15 percent in excess of
the normal span. This additional strength can be used in taking a samll angle of deviation on an intermediate tower, where the actual wind span is less than the design wind span. The angle of deviation to be taken in such cases is approximately given by:
θ =( wl /π T )x x180
Where w = total ind load per unit run of span length of all conductor
carried by the tower,
l = difference between the wind span used for design and the actual
wind span, and
T = the total maximum working tension of all conductors carried by the
tower.
*The weight span is the horizontal distance between the lowest point of the conductors, on the two spans adjacent to the tower . The lowest point is defined as the point at which the tangent to the sag curve, or to the sag curve produced, is horizontal. The weight span is used in the design of cross-arms.
| Is This Answer Correct ? | 3 Yes | 0 No |
what is the effect of back reactive power on the generator ?
WHAT IS THE DIFFERENCE BETWEEN AN ACB & mccb 7 WHAT IS THE CRITERIA WHEN TO USE WHICH OF THE TWO
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5PHASE
how many testing is necessary for 27 MVA transformer?
in our transmisison sub station why we step down firstly 132kv\33kv then 33kv to 11kv. can we direct step down 132kv to 11kv.
what is the impedence
What is the difference between Earth Fault protection & Neutral Protection
Efficient electrical earthing in hard rock area
how kva rating of transformer is calculated.
6 Answers Fluor Daniel, Siemens,
how to check the continuity of a cable with a megger
what is current actully?significance of current...not rate of change of flow.....
10. THE MOST COMMON TYPE OF THREE PHASE IN UNSYMMETRICAL FAULTS IS ........
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)