What are the different protection systems used to protect
the transformer internally and externally?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sankaralingam
i)Differential protection
ii)Restricted earth fault protection
iii)Buchholz relay
iv)Oil temperature indicator
v)Winding temperature indicator
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthikeyan
Bucholz relay
under voltage relay
over current relay
inverse time current over relay
pressure relay
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / viren89desai@yahoo.co.in
https://library.e.abb.com/public/4381d7d675f760cdc12575550081d599/AG03-5005E_en_Power_transformer_protection.pdf
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod g
Transformer protection
1) protection provided in the transformer are
A) buchholz relay for both main and oltc (ansi no 63)(alarm and trip)
B) winding temperature (wti) 49(alarm and trip)
C) oil temperature (oti) 49 (alarm and trip)
D) explosion vent or prv
e) Magnetic oil level gauge for alarm
f) Fire protection (Mulsifire system)
g) Lightning Arrester provided in both HV and LV
2) High Voltage side Protection
a) differential protection 87 (operate when fault occurs between HT CT and LV CT)
b) REF restricted earth fault 64 for winding protection
c) over flux for higher rating transformer
d) directional over current towards the source side, operate when fault feeding from LV during coupled with other transformer
NOTE: Master trip 86 relay is provided as the above relays are having less current rating output contacts, can not provide sufficient current huge trip coil circuit breaker. also 86 is provided with manual reset
3) Low voltage side Protection
Instantaneous and time delay over current 50
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avinash
Over current and earth fault Protection relay
Differential Protection relay
Restricted earth fault relay
oil temperature alarm & trip
Winding Temperature & trip
oil Level trip
buchhloz relay
oil surge relay
pressure relief device
HT breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imdad husen
IN TRANSFORMER PROTECTION IF HIGH INTERNAL FAULT OCCUR BETWEEN L.V.C.T.AND H.V.C.T. THEN DIFFERENTIAL RELAY SHOULD BE ORATED AND EXTERNAL FAULT OCCUR DIFFERENTIAL RELAY SHOULD NOT ORATED BECAUSE OF ZERO SEQUENCES CURRENT IS ABSENT
IN TRANSFORMER PROTECTION IF EXTERNAL FAULT OCCUR RESTRICTED EARTH FAULT RELAY SHOULD BE OPARTED
| Is This Answer Correct ? | 0 Yes | 1 No |
bus bar design conditions and sizing pls tell me quickly
What is the previous name of Cox's Bazar
what is the difference between contactors & relay.
What is the difference between IGBT and TRIAC?
During Testing of Maintenance Free Earthing, How deep should be the Spikes of Earth Test Meter should be inserted in the soil(one spike is 15 Meter & Other spike is 30 Mtrs away from the Main Earth Electrode. Because, recently, we observed that when spike is inserted 3-4 Inch in the earth- results are better, If spike is inserted 1 feet deep than results are increasing.
1. Synchronization is not required A. Thermal B.Hydel C.Wind D.Nuclear
2 Answers APGenco, Birla Power,
whatis the commertial spec. of distribution boards ?
can we synchronize star system generators with delta system transmission line ? and how ?
What are the types of TESTS in CIRCUIT BREAKERS based on Testing and commissioning?
What is VCB? where it is installed at SP. What is SP?
what is power factor ? how we can calculate the low power factor and amount of capacitor for improve that low factor ?
What should do when induction motor take more load in single phase ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)