What are the different protection systems used to protect
the transformer internally and externally?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sankaralingam
i)Differential protection
ii)Restricted earth fault protection
iii)Buchholz relay
iv)Oil temperature indicator
v)Winding temperature indicator
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthikeyan
Bucholz relay
under voltage relay
over current relay
inverse time current over relay
pressure relay
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / viren89desai@yahoo.co.in
https://library.e.abb.com/public/4381d7d675f760cdc12575550081d599/AG03-5005E_en_Power_transformer_protection.pdf
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod g
Transformer protection
1) protection provided in the transformer are
A) buchholz relay for both main and oltc (ansi no 63)(alarm and trip)
B) winding temperature (wti) 49(alarm and trip)
C) oil temperature (oti) 49 (alarm and trip)
D) explosion vent or prv
e) Magnetic oil level gauge for alarm
f) Fire protection (Mulsifire system)
g) Lightning Arrester provided in both HV and LV
2) High Voltage side Protection
a) differential protection 87 (operate when fault occurs between HT CT and LV CT)
b) REF restricted earth fault 64 for winding protection
c) over flux for higher rating transformer
d) directional over current towards the source side, operate when fault feeding from LV during coupled with other transformer
NOTE: Master trip 86 relay is provided as the above relays are having less current rating output contacts, can not provide sufficient current huge trip coil circuit breaker. also 86 is provided with manual reset
3) Low voltage side Protection
Instantaneous and time delay over current 50
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avinash
Over current and earth fault Protection relay
Differential Protection relay
Restricted earth fault relay
oil temperature alarm & trip
Winding Temperature & trip
oil Level trip
buchhloz relay
oil surge relay
pressure relief device
HT breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imdad husen
IN TRANSFORMER PROTECTION IF HIGH INTERNAL FAULT OCCUR BETWEEN L.V.C.T.AND H.V.C.T. THEN DIFFERENTIAL RELAY SHOULD BE ORATED AND EXTERNAL FAULT OCCUR DIFFERENTIAL RELAY SHOULD NOT ORATED BECAUSE OF ZERO SEQUENCES CURRENT IS ABSENT
IN TRANSFORMER PROTECTION IF EXTERNAL FAULT OCCUR RESTRICTED EARTH FAULT RELAY SHOULD BE OPARTED
| Is This Answer Correct ? | 0 Yes | 1 No |
how to caculate no load loss, load losses & impedance percentage in power or distribution transformers
line and phase voltage relationship?
why all selected supply voltages are multiple of 11.i.e440,11 kv,33 kv,66 kv,110 kv etc
why PD testing for power cables
1 Answers Bhushan Power Steel, CSE, Datre Corporation,
Tell me how you are ready to comply with the employment rules and regulations if your CV is considered for employment?
what is the Pickup/drop off ratio in BCPU relays
high voltage transformer input voltage,current and amps rating..distributed transformer input voltage,current and amps rating...
why Induction Generators are not "Black start" ? and apart from WTGs where this types of generator are generally used?
Why we cant store an ac power. If we coo store in which device we can?
I am working as maintenance engg. in electrical but i want to do carrier in electrical drawing.Tell me about that.
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
How to calcualte 1unit of current consumption?
3 Answers Bhushan Power Steel, ITC Infotech,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)