What are the different protection systems used to protect
the transformer internally and externally?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sankaralingam
i)Differential protection
ii)Restricted earth fault protection
iii)Buchholz relay
iv)Oil temperature indicator
v)Winding temperature indicator
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthikeyan
Bucholz relay
under voltage relay
over current relay
inverse time current over relay
pressure relay
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / viren89desai@yahoo.co.in
https://library.e.abb.com/public/4381d7d675f760cdc12575550081d599/AG03-5005E_en_Power_transformer_protection.pdf
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod g
Transformer protection
1) protection provided in the transformer are
A) buchholz relay for both main and oltc (ansi no 63)(alarm and trip)
B) winding temperature (wti) 49(alarm and trip)
C) oil temperature (oti) 49 (alarm and trip)
D) explosion vent or prv
e) Magnetic oil level gauge for alarm
f) Fire protection (Mulsifire system)
g) Lightning Arrester provided in both HV and LV
2) High Voltage side Protection
a) differential protection 87 (operate when fault occurs between HT CT and LV CT)
b) REF restricted earth fault 64 for winding protection
c) over flux for higher rating transformer
d) directional over current towards the source side, operate when fault feeding from LV during coupled with other transformer
NOTE: Master trip 86 relay is provided as the above relays are having less current rating output contacts, can not provide sufficient current huge trip coil circuit breaker. also 86 is provided with manual reset
3) Low voltage side Protection
Instantaneous and time delay over current 50
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avinash
Over current and earth fault Protection relay
Differential Protection relay
Restricted earth fault relay
oil temperature alarm & trip
Winding Temperature & trip
oil Level trip
buchhloz relay
oil surge relay
pressure relief device
HT breaker
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imdad husen
IN TRANSFORMER PROTECTION IF HIGH INTERNAL FAULT OCCUR BETWEEN L.V.C.T.AND H.V.C.T. THEN DIFFERENTIAL RELAY SHOULD BE ORATED AND EXTERNAL FAULT OCCUR DIFFERENTIAL RELAY SHOULD NOT ORATED BECAUSE OF ZERO SEQUENCES CURRENT IS ABSENT
IN TRANSFORMER PROTECTION IF EXTERNAL FAULT OCCUR RESTRICTED EARTH FAULT RELAY SHOULD BE OPARTED
Is This Answer Correct ? | 0 Yes | 1 No |
different aspects of voltage stability
State nyquist stability criterion.
power 148kw i need exat cable size in 148 kw in 3phase what size of cable can i used.
When we give supply to a transformer 11 kv and we get 415v from it, so when we give supply to same transformer 415v on ht side what we get? and When we gives supply to any transformer to L.T. side 415v or 220v What supply is on H.T. side?
What is difference between miniture circuit breaker and module case circuit breaker up to 63Amp.
Electrical Engineering
0 Answers Gamesa, Medha Servo,
What do you understand by avr?
is the secondary voltage of current transformer greater than primary voltage,,,,,,,,] give the example with ct burden,current ratio,and primary and secondary side voltage?
Why transformer use to generator neutral earthing purpose ?
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
how to protect motor in dol starter having capacity of 30 hp.40 hp?