What are the different protection systems used to protect
the transformer internally and externally?
Answer Posted / vinod g
Transformer protection
1) protection provided in the transformer are
A) buchholz relay for both main and oltc (ansi no 63)(alarm and trip)
B) winding temperature (wti) 49(alarm and trip)
C) oil temperature (oti) 49 (alarm and trip)
D) explosion vent or prv
e) Magnetic oil level gauge for alarm
f) Fire protection (Mulsifire system)
g) Lightning Arrester provided in both HV and LV
2) High Voltage side Protection
a) differential protection 87 (operate when fault occurs between HT CT and LV CT)
b) REF restricted earth fault 64 for winding protection
c) over flux for higher rating transformer
d) directional over current towards the source side, operate when fault feeding from LV during coupled with other transformer
NOTE: Master trip 86 relay is provided as the above relays are having less current rating output contacts, can not provide sufficient current huge trip coil circuit breaker. also 86 is provided with manual reset
3) Low voltage side Protection
Instantaneous and time delay over current 50
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
How to decide and select the different earthing wire size for the different types of earthing
What are operating procudures & Safety precautions to be observed while operating OLTC in manual mode ?
could you measure current in parallel?
What is shunt voltage and u v voltage witch one best
Disadventage of cable-gland earthing if any ?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what is the easiest method of short circuit current calculation ? pls. derive with a mathematical example in real life application.
what is the path of thunderlightening? once both a buffalo and a person were standing 5m apart but lightening hit and killed buffalo not person?
Why electrical power generation and transmission done in 3 phase system not more than 3 phase ?
who invented active elements? plz give me the complte details of active elements...
Hi I'm doing my MBA(3rd semester).I applied for the post of ET conducted by BHEL the last year.I cleared the written and lost in personal interview.Again I wrote the exam this time and cleared the written n yet to take the personal interview.Shall I disclose in the interview about my studies.What shall i say if they ask about my change from studies to job
How to select a transformer group to connect a 0,433 KV generation with 33 KV grid in bi directional flow of current
what are your career plans upon completion of the programme and the relevance of recity generation to your professional development?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What is the technical difference between On delay timer and a Star delta timer?