why when i start my diesel generator it takes 1 minute or less then stop, and i checked the oil sensor is ok and when the generator start i can get 220 voltage but it it is stop after 1 minute or less, how can i solve this problem?
Answer / m.r.chaudhari
Check bettery & bettery charger.
When bettery is discharge due to not working properly battery charger.
| Is This Answer Correct ? | 0 Yes | 0 No |
Fault current shall be part of tech specs of power cable or not?.
what are the standard values for resistances(Megger testing) between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.
when conductor rotates in varying magnetic field the emf will induced in it and it is sinusoidal in nature ...? Why it is not in square wave and rectangular wave in nature?
how on load transformer is chnage the Tapping ?
what is the meaning of spur line?
Why are calling lagging power factor is a inductive load?
how to do CT Burden test
sir vizag steel ka junior trainee ka paper kitne number ka ayega
Main CT ration is 400/5, meter CT ratio is open type: -/5A. What is the Multiplying factor of the meter, considering same PT ratio.
why do we use UPF watt meter in short circuit test of the transformer and LPF watt meter in open circuit test of the transformer
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)