10rm cable can got load ---- amp?
Or
Which Size Cable can take the load 100amp capacity SCR; breaker.
Answer / babar bilal
100 Amp load can be beard by a 50mm² cable easily. Its current carrying capacity is 155 Amps. If you go down a bit, then 35mm² cable can carry 94 Amps maximum, but its safe limit as per standards is 75.2 AMps @ 80% load capacity.
Is This Answer Correct ? | 1 Yes | 0 No |
Do we really need wheels for the transformer
How shall i design a liquid rotor starter
sir, 3phase induction motor takes different pf and different KW in three phase while running,explain reason
when voltage gets down the current of motor increases. but according to Ohm's law voltage is directly proportional to current. plz explain
4 Answers Maruti Suzuki, TATA,
In all the generators, the excitation supply is DC. What is the significance of DC excitation? What will happen if AC supply is given as excitation supply?
If I want to connect a capacitor bank on the HT side of a 11kV/415V, 3 phase delta-star distribution transformer to supply Reactive power to it..what practical specifications of a Capacitor bank that can i've??please reply..
if u give d.c. supply to transformer primary then what happen.&why??????????????
Whot is the braking capacity for MCCB. How we select different braking capacity.
how to avoid Saturation in C.T?
i applied for c licence with my one year apperents trainee and i have attaced with A grade contractor company experiance that is for 14 monts experiance this document is sufeicant for c licence? pls tell why they rejected
0 Answers TNEB Tamil Nadu Electricity Board,
We wish to test 60 Hz systems from a 50 Hz supply. To acheive frequency conversion, we use a VFD. The VFD powers 40 kVA transformer, which has motor and non-motor loads on it. Will the transformer work?
why the Different manufacture's rating of Gas genset are different? i.e : cummins genset rating is in KVA .( 625kv). While GE- Jenbacher make genset have rating in Kw. (625 kw)