Answer / babar bilal

100 Amp load can be beard by a 50mm² cable easily. Its current carrying capacity is 155 Amps. If you go down a bit, then 35mm² cable can carry 94 Amps maximum, but its safe limit as per standards is 75.2 AMps @ 80% load capacity.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Do we really need wheels for the transformer

1 Answers  


How shall i design a liquid rotor starter

0 Answers  


sir, 3phase induction motor takes different pf and different KW in three phase while running,explain reason

0 Answers   UltraTech,


when voltage gets down the current of motor increases. but according to Ohm's law voltage is directly proportional to current. plz explain

4 Answers   Maruti Suzuki, TATA,


In all the generators, the excitation supply is DC. What is the significance of DC excitation? What will happen if AC supply is given as excitation supply?

2 Answers  






If I want to connect a capacitor bank on the HT side of a 11kV/415V, 3 phase delta-star distribution transformer to supply Reactive power to it..what practical specifications of a Capacitor bank that can i've??please reply..

0 Answers  


if u give d.c. supply to transformer primary then what happen.&why??????????????

4 Answers   DCS, DRDO, HCL,


Whot is the braking capacity for MCCB. How we select different braking capacity.

1 Answers  


how to avoid Saturation in C.T?

0 Answers  


i applied for c licence with my one year apperents trainee and i have attaced with A grade contractor company experiance that is for 14 monts experiance this document is sufeicant for c licence? pls tell why they rejected

0 Answers   TNEB Tamil Nadu Electricity Board,


We wish to test 60 Hz systems from a 50 Hz supply. To acheive frequency conversion, we use a VFD. The VFD powers 40 kVA transformer, which has motor and non-motor loads on it. Will the transformer work?

2 Answers   Suzlon,


why the Different manufacture's rating of Gas genset are different? i.e : cummins genset rating is in KVA .( 625kv). While GE- Jenbacher make genset have rating in Kw. (625 kw)

1 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)