Boiler flame scanner working principle?
in sports(eg,cricket) what is the technique for measurement of speed of the ball thrown by the bowler.
a flow transmitter [range-0-400mbar] connected in process line. please explain me how to calibrate the flow transmitter , & how to do static error
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
how does pressure is converted into milli amps in pressure transmitter? plzzz explain practically
Reasons for using seal pots:
what is "smart" in smart transmitter ?
Square root calculation for dp flow transmitter?
what is the standard of determining opening/closing time of Motor Operated Valve?
what is commissioning.
Instrumentation Safe Guarding test. How to determine the interval time of the test. eg:Halfyearly,Every year,Every three years etc.
what is the diffrence between pressure safety valve & pressure relief valve....pls
what is the difference between dcs & plc