Answer / narayan
Check Tx data sheet or engraved plate on the tx and it gives span limit as 2000mm, then we can change
if it is below 2000 mm, we can not change, or calibrate
it is sensor range
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mudassir
yaa you can but you have check the model no. if it is30512G
THEN YOU CAN CALIBRATE IT upto6000mmwc
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / saumil
We connect 375hart protocol and given this new range and calibrate 20 mA at 2000mmwc
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ramana
If the Tx. Range is 2000 mmWC we can change it. But we need
little calculation. There is one formula
square root of(P1/P2)= Q1/Q2
Where P1= Pressure 1
P2= Pressure 2
Q1= Flow at Pressure 1
Q2= Flow at Pressure 2
Is This Answer Correct ? | 0 Yes | 6 No |
what is concept of field,control room area in transmitters?
Steve said that "An eddy-current probe works by passing an alternating current through a coil of wire and measuring the coil’s impedance" while we are using -24 Volt DC , So I am confused about DC and AC. Plz .
2 Answers Jindal, Sadara Chemicals,
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
what is see back effect?
Distributed control system
what is flow
Hi..i am B.E. (elect.&comm.)..i m workini in a bio mass power plant as inst. Engg. I want 2 know about growth in big power plant sector..is this field is good 4 me ..i m electronics engg..? Plz plz reply..
How to measure the vibration..?
Why Instrumentation Air Compressor called as Instrumentation Air compressor?pls dont just tell its trasferring IA to all transmitter,valves.I need exact reason, please......................
yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculation result is bad) in manual they mentioned reasion That the output goes to the value set by hardware failure mode jumper. How can solve this problem ? anybody can say solution
What is the meaning of Dry contact and Wet Contact related to to sensors?
why using negative supply for bentley nevada vibration system ?