Why is the length of cable layyed from RTD to temp. Transmitter should be minimum? Why does heating effect takes place in their?
Why is the length of cable layyed from RTD to temp. Transmitter should be minimum? Why does
heating effect takes place in their?
An RTD develops a very low voltage signal, on the order of tenths of a volt. Low level signals on
that magnitude can be overwhelmed by industrial electrical noise. And voltage signals, unlike a
current loop signal, diminishes (decreases) over distance.
There is also a limitation on the maximum wire resistance (which is proportional to wire length
and gauge) that an RTD input on a temperature transmitter or controller analog input can handle.
These reasons are why RTD temperature transmitters are so popular; the transmitter connects
close to the RTD minimizing noise and producing a current loop signal that is relatively immune to
noise and that does not decay over distance. The loop power is delivered over the same to two
wires as the output signal uses.
The self-heating effect is at the RTD element itself, it is not in the extension wire/cable
Unless it's a cryogenic (low temperature) application, the self heating effect is usually ignored.
Look at how little heat is developed:
A 1ma (0.001A) excitation current through 120 ohms (approx 52 Deg C) drops 0.120V (E = IR)
0.120V * 0.001A = 0.00012W or 120uW or 0.12mW
That's not a lot of heat to dissipate.
Carl Ellis
Measure First
| Is This Answer Correct ? | 6 Yes | 0 No |
what is DCS and SCADA?
what is the difference b/w normal thermocouple and skin type thermocouple?
How can measure flow in oil line?which type of transmitter is generally used?
What is cut off relay? And why use in PLC and DCS?
plz tell me clearly about PID.."when v have to change I value,D value,GAIN??
i want to know the interview format fot gail, instrumentation. pls answer me in habib.sami1003@gmail.com
what are the selections available in configuring a burnout protection of a controller? thanks
0 Answers NPC Alliance Corporation,
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
which instrument is used to study the structure of phloem and xylem tissue?
why we are using ungrounded RTD sensor and what is difference between grounded RTD and Ungrounded?
1.In which princeple DP transmeter works? 2.Why UPS system is use for DCS? 3.How drum lvel controller works? 4.What is the difference between glob valve and gate valve? 5.How axial shift probe work & in which princeple it works?
1 Answers Luberef, Qatar Gas, Reliance,
WHAT IS THE MAIN WORKING OF BOILER.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)