Transformer calculation
Answer / faiyaz
We know that, Transformer always rated in kVA. Below are two simple formulas to find the rating of Single phase and Three phase Transformers.
Rating of Single Phase Transformer:
P = V x I.
Rating of a single phase transformer in kVA
kVA= (V x I) / 1000
Rating of a Three Phase Transformer:
P = √3. V x I
Rating of a Three phase transformer in kVA
kVA = (√3. V x I) /1000
but lets me try to explain.
Here is the rating of Transformer is 100kVA.
But Primary Voltages or High Voltages (H.V) is 11000 V = 11kV.
And Primary Current on High Voltage side is 5.25 Amperes.
Also Secondary voltages or Low Voltages (L.V) is 415 Volts
And Secondary Current (Current on Low voltages side) is 139.1 Amperes.
In simple words,
Transformer rating in kVA = 100 kVA
Primary Voltages = 11000 = 11kV
Primary Current = 5.25 A
Secondary Voltages = 415V
Secondary Current = 139.1 Amperes.
Now calculate for the rating of transformer according to
P=V x I (Primary voltage x primary current)
P = 11000V x 5.25A = 57,750 VA = 57.75kVA
Or P = V x I (Secondary voltages x Secondary Current)
P= 415V x 139.1A = 57,726 VA = 57.72kVA
Once again we noticed that the rating of Transformer (on Nameplate) is 100kVA but according to calculation…it comes about 57kVA…
The difference comes due to ignorance of that we used single phase formula instead of three phase formula.
Now try with this formula
P = √3 x V x I
P=√3 Vx I (Primary voltage x primary current)
P =√3 x 11000V x 5.25A = 1.732 x 11000V x 5.25A = 100,025 VA = 100kVA
Or P = √3 x V x I (Secondary voltages x Secondary Current)
P= √3 x 415V x 139.1A = 1.732 x 415V x 139.1A= 99,985 VA = 99.98kVA
Consider the (next) following example.
Voltage (Line to line) = 208 V.
Current (Line Current) = 139 A
Now rating of the three phase transformer
P = √3 x V x I
P = √3 x 208 x 139A = 1.732 x 208 x 139
P = 50077 VA = 50kVA
| Is This Answer Correct ? | 4 Yes | 0 No |
what do you mean by puncturing of insulator by ice -coating?
An ISP is granted a block of addresses starting with 150.80.0.0/16. The ISP wants to distribute these blocks to 2600 customers as follows. a) 200 medium size businesses; each needs 16 addresses b) 400 small businesses; each needs 8 addresses c) 2000 households; each needs 4 addresses Design the subblocks and give the slash notation for each subblock. Find out how many addresses are still available after these allocations.
How can we choose the rating of submersible motors
what are the differance between neutral and earthing?
If rotor works in clock wise what happens
How to determine the Power factor is Leading,Lagging & Unity ?.I don'thave any Meters.
what is the purpose finding power factor?
What value of resistance required between Saftey earth and instrunment earth , maximum and minimum values required
How the unidirectional torque produced in dc motor
where any change in supply line due to the incipient faults in three phase induction motor
why transformer are rated in kva.
Transformers with dc supply
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)