Transformer calculation
Answer / faiyaz
We know that, Transformer always rated in kVA. Below are two simple formulas to find the rating of Single phase and Three phase Transformers.
Rating of Single Phase Transformer:
P = V x I.
Rating of a single phase transformer in kVA
kVA= (V x I) / 1000
Rating of a Three Phase Transformer:
P = √3. V x I
Rating of a Three phase transformer in kVA
kVA = (√3. V x I) /1000
but lets me try to explain.
Here is the rating of Transformer is 100kVA.
But Primary Voltages or High Voltages (H.V) is 11000 V = 11kV.
And Primary Current on High Voltage side is 5.25 Amperes.
Also Secondary voltages or Low Voltages (L.V) is 415 Volts
And Secondary Current (Current on Low voltages side) is 139.1 Amperes.
In simple words,
Transformer rating in kVA = 100 kVA
Primary Voltages = 11000 = 11kV
Primary Current = 5.25 A
Secondary Voltages = 415V
Secondary Current = 139.1 Amperes.
Now calculate for the rating of transformer according to
P=V x I (Primary voltage x primary current)
P = 11000V x 5.25A = 57,750 VA = 57.75kVA
Or P = V x I (Secondary voltages x Secondary Current)
P= 415V x 139.1A = 57,726 VA = 57.72kVA
Once again we noticed that the rating of Transformer (on Nameplate) is 100kVA but according to calculation…it comes about 57kVA…
The difference comes due to ignorance of that we used single phase formula instead of three phase formula.
Now try with this formula
P = √3 x V x I
P=√3 Vx I (Primary voltage x primary current)
P =√3 x 11000V x 5.25A = 1.732 x 11000V x 5.25A = 100,025 VA = 100kVA
Or P = √3 x V x I (Secondary voltages x Secondary Current)
P= √3 x 415V x 139.1A = 1.732 x 415V x 139.1A= 99,985 VA = 99.98kVA
Consider the (next) following example.
Voltage (Line to line) = 208 V.
Current (Line Current) = 139 A
Now rating of the three phase transformer
P = √3 x V x I
P = √3 x 208 x 139A = 1.732 x 208 x 139
P = 50077 VA = 50kVA
Is This Answer Correct ? | 4 Yes | 0 No |
1) name the communication cable and how it is communicate in between plc to modbus , plc with hmi? 2)name of the communication cables?
In 400KV Switchyard, we have used Circuit Breaker With PIR, what is the significance of PIR & why they'r used?
Sir, I completed DEEE... And now I working in TNEB for one year apprenticeship. If I eligible for applying c license and how can I get?
if we use contactor & MCCB both in a feeder.in this feeder rating of contactor is higher or lower or same of MCCB rating & why?
If NO contact of relay gets supply from other sources or other part of circuit and at a time relay coil activates,then current will flow in which direction & will it cause to damage relay??
At light load transformer efficiency is less because A secondary output is low B transformer losses are high C fixed loss is high compared to output D copper loss is small
why mosquito bat makes noise when it hits with a insect?
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
why single phase induction motors are not self staring ? how can we start the 1-phase Induction motor ?
how to select fuse rating for a 3-phase motor ???
What is the function of pulse transformer?
Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million