how to calibrate TT transmitter
Answers were Sorted based on User's Feedback
Disconnect the field sensor.
Connect a calibrated/traceable temperature signal calibrator.
Apply LRV value.
Trim the 4.0mA output.
Apply the URV value.
Trim the 20.0mA output.
Check as many interim points as the calibration protocol requires and note the output and the deviation from the expected value.
Determine whether the transmitter is within spec from the deviation values seen.
If transmitter passes, reconnect the field sensor to the input.
Fill in the paperwork.
Carl Ellis
Measure First
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / eid elatawy
First i have to know the connected element
1. RTD :using resistance box and divide the range into 4 quarters for example the range 0 to 100 deg we have 0,25,50,75,100 will find the related resistance from the table and see the transmitter output and if any deviation will make trim zero and span trim.
2. TC the same idea but we use MV supply and by using TC tables.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / karishma
First do span and zero adjustment of a temperature transmitter. Then when the input signal is zero the output is 4mA if not readjust the span and zero again provide 25% 50% 75% 100% Signal and see the output it should give 20 mA for 100% signal input.
| Is This Answer Correct ? | 1 Yes | 0 No |
Can we used Condensate Pot on flow transmitter which is using on liquid having sluge and DP transmitter is in pit and below the process line,Can we used Condensate pot for accamulate the Sluge?
I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow measurement so whats the formula.
How to gennerate earth leakage monitoring alarm for solenoid valves in control system?
how to check thermocouple ,its working or not?
14 Answers Coca Cola, Ford, Honeywell,
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer.
difference between accuracy and precision
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
what is hart communicater? can u give brief explanation about this issue?
how to tune the closed pid loop?
Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000
give some question relative instrument fitter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)