There is 15 KVA UPS using for single phase load.And 30
batteries of 12 V, 100 Ah are connected in series. Load is
taking 15 A current.What will be the back up power for this
UPS on same load?
Is it correct that batteries are connected in series ? The stored energy in each battery is 12 x 100 = 1200 Wh. Total = 36000Wh . The load in watts = 230 x 15 = 3500W ( app ) . Back up = 36000/ 3500 = 10 hr(app)
| Is This Answer Correct ? | 2 Yes | 0 No |
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
What is a soft start?
Hello sir. if u have electical engineering exam paper then plz mail me at bhumika_1187@yahoo.co.in. i m appearing exam for HPCL.
in Telecom DC system-why positive +ve is made earthed.and - ve is fed to load.
Why we can not get 100% efficiency from a Gas Generator?
What is the type of earth fault protection used in battery? explain.
Draw a 230kv two-bus bar system showing the following. 1.Two generators (150MW) each connected through one 15.75/230KV transformers 2. 1 outgoing lines 3. Two 230/130 KV transformers 4. BUS PT's 5. CT
when two gen set runing in parallel but thay have diffrent pole pitch, then what will be happan
what do you call the last pole on a overhead line near a substation
How to convert resistance value at 20 degree to 90 degree?
DESCRIBEPNEUMATIC SYSTM OF ASH HANDLING PLANT
Why inverter rating in KVA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)