There is 15 KVA UPS using for single phase load.And 30
batteries of 12 V, 100 Ah are connected in series. Load is
taking 15 A current.What will be the back up power for this
UPS on same load?

Answer Posted / k.prakashchandra

Is it correct that batteries are connected in series ? The stored energy in each battery is 12 x 100 = 1200 Wh. Total = 36000Wh . The load in watts = 230 x 15 = 3500W ( app ) . Back up = 36000/ 3500 = 10 hr(app)

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is knee point voltage of transformer?

679


cc of scorpio?

1797


What is resolution of a measurement?

739


If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?

943


How can we findout the maximum efficiancy of Transformer? At which load?

1612






In power transmission using open belts or horizontal shafts it is preferable to have the slack side of the belt on the top because

777


Difference between shunt, PMG and AREP excitation. Which is the most reliable between PMG and AREP.

9026


What is principle of Floroscent tube 36watt.

1582


What is core CT & it's function?

1634


The synchronous machine excitation system explain

1333


This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.

2016


What is force on parallel conductors ?

649


Define closed loop control system.

654


Write down the design procedure of commutaj.

1730


Where can I get CPWD electrical specifications & Shedule of rates? Please help me

1816