Is it possible to make 0.75KW motor earthing from MCC panel by
using the 1.5 SQMM, 4 core cable, means 3 core for 3 Phases &
1 core for Earth terminal?
Answers were Sorted based on User's Feedback
Answer / najam sultan
For earthing we don't need to use 4 cores, only a single core is enough for earthing.And 1.5sqmm single core cable is enough for earthing of 0.75 kW motor.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / avd
Yes it can be done.Do not worry for fault level because it
will be greaty reduced due to lowersize cable.But make sure
you have installed earth fault protection device to isolate
incase of earth fault.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mukesh
For motor we need to use 3 cores, only a single core is
enough for earthing.And 1.5sqmm single core cable is enough
for earthing of 0.75 kW motor and double earth is
requirements for whereas 3 phases is used as per rule.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jyotiranjan sahoo
Yes it can use 1.5 sqmm cable of earthing for that motor but in Indian standard we must be use another body earthing
| Is This Answer Correct ? | 0 Yes | 0 No |
for 8 mva 33/11 kv transformer what will be the setting of differential relay on which it trip & what is the HF setting in this relay
How to use a insulation resistance tester on a three phase electric motor?
Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.
What should the transformer connection of a 11/220 kV step up and 66/11 kV step down transformer ?
State how to produce a constant rotating field by application of alternating currents to stator armature of a three-phase squirrel-cage induction motor
What is the Surge suppresor? Why using in a UDB's and How it works?
can you any one give exact mathematical relation between AC current and DC current?
why one side of tubelight glows after switch off ?
What happen to generator if i have unbalanced load?
0 Answers Reliance Energy, Sail, TCS,
transmisancy eficencey calculation formula
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
what will happen when excitation of a synchronous machine is suddenly reduce to zero when it is running at full load..??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)