i want the equation of this question.
Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer: 239.2 mmH2O
Present max flow rate = 1700 nm3/hr
Present max DP (at max flow rate) = 120 mm H2O
New max flow rate = 2400 nm3/hr
New max DP (at new max flow rate) = x
2400/1700 = 1.412 or an increase of 141.2% in flow rate.
The DP and the flow rate relationship is a square root relationship, but the calculation is based on normalized percentage.
X = 1.412^2*120
X = 1.993*120
X = 239.2 mmH2O
The increase in max DP from 120 to 239.2 mmH2O is an increase of
239.2/120 = 1.993 or 199.3% increase in max DP at max flow rate.
Sq root of 1.993 = 1.412 or 141.2% increase in max flow rate (2400/1700)
Carl Ellis
Measure First
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / alim
I think the equation is not straight forward, you need some repetition formula for calculating this.
Normally, I will use some software to do this kind of calculation such as InstruCalc. The data that you presented in the question is not enough. I am assuming that you are using the orifice in as the flow element, then you still need viscosity and specific gravity of the fluid.
Is This Answer Correct ? | 1 Yes | 1 No |
1. What is the main differences between GE Mark IV and Mark V Turbine Control System? 2. what is the main differences between GE Mark V and Mark VI?
my data card only does run in my mobile so how can change it that it run other mobile & computer and i can stor data in my data card
why we are using digital signals for I/O & how to measure this signals is getting or not ?
Why we use negetive (-)voltage in vibration system
-200mmwc to 500mmwc range transmitter have there 4mA is -200 and 20mA is 500.what is the range in 12mA?
how many type conductivity sensor ?
What is an SCR?
What s PDS & PDMS tools ?its role in instrumentation?
Sitrans LR460 Radar level transmitter getting level out or disturbed level during moisture present in the material ie coal in the pccb bunker in CHP.Any suggestions for this problem...????
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
send me HPCL paper
we re giviang 24v supply to transmitter and we getting output from tx?now my question is wht we call this complete proces?