i want the equation of this question.
Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer: 239.2 mmH2O
Present max flow rate = 1700 nm3/hr
Present max DP (at max flow rate) = 120 mm H2O
New max flow rate = 2400 nm3/hr
New max DP (at new max flow rate) = x
2400/1700 = 1.412 or an increase of 141.2% in flow rate.
The DP and the flow rate relationship is a square root relationship, but the calculation is based on normalized percentage.
X = 1.412^2*120
X = 1.993*120
X = 239.2 mmH2O
The increase in max DP from 120 to 239.2 mmH2O is an increase of
239.2/120 = 1.993 or 199.3% increase in max DP at max flow rate.
Sq root of 1.993 = 1.412 or 141.2% increase in max flow rate (2400/1700)
Carl Ellis
Measure First
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / alim
I think the equation is not straight forward, you need some repetition formula for calculating this.
Normally, I will use some software to do this kind of calculation such as InstruCalc. The data that you presented in the question is not enough. I am assuming that you are using the orifice in as the flow element, then you still need viscosity and specific gravity of the fluid.
| Is This Answer Correct ? | 1 Yes | 1 No |
Different between control valve and mov
How to do calibration of magnetic flowmeter
what is the thermocuple compensation circuit
How can we cheak the ENCODER ?
how to relay switch sense the fault?
What is the difference between rich gas and lean gas?
In E&I diagram what is the meaning of rectangular box and circular box
I have a steam flow DP transmitter that has output swinging. Steam valve is in manual.I have good steam pressure. The impulse lines have steam tracing on them. The steam tracing has a hole in it that is blowing raw steam on the high side impulse line only. Could this be causing the swinging?
can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).
what is all types of analyzer in water production plant?
why temperature transmitter is showing ambienttemp.but 21.5ma. alarm AO showing at the display &how to sloves this problem.
in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)