Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


flow transmitter range is 0 -500 mmwcc but the transmitter
shows 12 ma for o mmwc instead of 4 ma ...how to solve this
problem when we apply 375 mmwc it shows 16 ma

Answers were Sorted based on User's Feedback



flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...

Answer / satya

1st ensure the tapping . the root valve. orifice range . tx range . then open the high side , open the low side drain the flow shoude be zero . if not trim the tx. and then. take it online

Is This Answer Correct ?    7 Yes 2 No

flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...

Answer / dinesh

the transfer function should have been square root but the transfer function mentioned is linear which is as follows

y=mx+c where m is slope & c is the bias
to calculate slope
m={(y2-y1)/(x2-x1)} where
y2=16ma; y1=12 ma; x2=375 mmwc; x1=0 & C is 12ma at 0 mmwc

so y= (4/375)*x + 12

in order to get correct flow change the transfer function to square root in Tx

Is This Answer Correct ?    2 Yes 0 No

flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...

Answer / ghanshyam

brother also check its sqrt or linier

Is This Answer Correct ?    2 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

why we are using pnp npn for sensors is there any other type?

1 Answers   CGL,


Sir , i have completed my M.Sc In Instrumentation and presently working in Maintenance department 3 yrs Exp , is there is any possible for work in offshore ..

0 Answers  


If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?

0 Answers  


Steve said that "An eddy-current probe works by passing an alternating current through a coil of wire and measuring the coil’s impedance" while we are using -24 Volt DC , So I am confused about DC and AC. Plz .

2 Answers   Jindal, Sadara Chemicals,


We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???

2 Answers   National Petrochemical Company,


Explain about safety integrated level protection? . How it was differ from other protections ?

0 Answers  


what is the essential difference between DIODE and SCR in term of application.

2 Answers   ADMA OPCO,


What is loop or pigtail in an impulse line?

8 Answers   Qatar Airlines, Qatar Petroleums,


why gray colour is choosing to all instrument panel.why not choosing other colour?

1 Answers   Reliance,


What is cascade control in process instrumentation?

4 Answers   Engineers India, ITC Infotech,


What is the maximum distance limit of 4-20mA and 0-10V DC standard signal transmission ?

3 Answers   BARC, ME,


how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)