flow transmitter range is 0 -500 mmwcc but the transmitter
shows 12 ma for o mmwc instead of 4 ma ...how to solve this
problem when we apply 375 mmwc it shows 16 ma
Answers were Sorted based on User's Feedback
Answer / satya
1st ensure the tapping . the root valve. orifice range . tx range . then open the high side , open the low side drain the flow shoude be zero . if not trim the tx. and then. take it online
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / dinesh
the transfer function should have been square root but the transfer function mentioned is linear which is as follows
y=mx+c where m is slope & c is the bias
to calculate slope
m={(y2-y1)/(x2-x1)} where
y2=16ma; y1=12 ma; x2=375 mmwc; x1=0 & C is 12ma at 0 mmwc
so y= (4/375)*x + 12
in order to get correct flow change the transfer function to square root in Tx
Is This Answer Correct ? | 2 Yes | 0 No |
should I use Hydrostatic Pressure Transmitter for measurement of DENSITY of filled tank ? If YES then please explain how.
How I identify to solonied coil which is 24v or 230v In our lab.because there is no tag.
1 Answers MRPL Mangalore Refinery and Petrochemicals Limited,
why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.
why do we use 4-20 ma current why cant o-20ma
what is linerity and non-linearity?
why is an oxygen sensor used in a boiler stack
What are Sinking and Sourcing IO Cards
How do understand by hart protocol?
4 Answers BW Instrumentation Electrical,
Hi Friends i am going to write BARC written test by this month 20th (20-5-2008). So please if any body knows the details about this or having previous question papers pls mail me to kkumarei@gmail.com. For Suggestions give one message to 9962122264
how many types of sensor in instrumentation
How to convert ma to mv? Resistance 250 ohm is connected in series or Parallel?
sir, give me placement papers and interview quistion of birla group company of copper.