flow transmitter range is 0 -500 mmwcc but the transmitter
shows 12 ma for o mmwc instead of 4 ma ...how to solve this
problem when we apply 375 mmwc it shows 16 ma
Answers were Sorted based on User's Feedback
Answer / satya
1st ensure the tapping . the root valve. orifice range . tx range . then open the high side , open the low side drain the flow shoude be zero . if not trim the tx. and then. take it online
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / dinesh
the transfer function should have been square root but the transfer function mentioned is linear which is as follows
y=mx+c where m is slope & c is the bias
to calculate slope
m={(y2-y1)/(x2-x1)} where
y2=16ma; y1=12 ma; x2=375 mmwc; x1=0 & C is 12ma at 0 mmwc
so y= (4/375)*x + 12
in order to get correct flow change the transfer function to square root in Tx
| Is This Answer Correct ? | 2 Yes | 0 No |
why we are using pnp npn for sensors is there any other type?
Sir , i have completed my M.Sc In Instrumentation and presently working in Maintenance department 3 yrs Exp , is there is any possible for work in offshore ..
If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?
Steve said that "An eddy-current probe works by passing an alternating current through a coil of wire and measuring the coil’s impedance" while we are using -24 Volt DC , So I am confused about DC and AC. Plz .
2 Answers Jindal, Sadara Chemicals,
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,
Explain about safety integrated level protection? . How it was differ from other protections ?
what is the essential difference between DIODE and SCR in term of application.
What is loop or pigtail in an impulse line?
8 Answers Qatar Airlines, Qatar Petroleums,
why gray colour is choosing to all instrument panel.why not choosing other colour?
What is cascade control in process instrumentation?
4 Answers Engineers India, ITC Infotech,
What is the maximum distance limit of 4-20mA and 0-10V DC standard signal transmission ?
how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)