flow transmitter range is 0 -500 mmwcc but the transmitter
shows 12 ma for o mmwc instead of 4 ma ...how to solve this
problem when we apply 375 mmwc it shows 16 ma
Answers were Sorted based on User's Feedback
Answer / satya
1st ensure the tapping . the root valve. orifice range . tx range . then open the high side , open the low side drain the flow shoude be zero . if not trim the tx. and then. take it online
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / dinesh
the transfer function should have been square root but the transfer function mentioned is linear which is as follows
y=mx+c where m is slope & c is the bias
to calculate slope
m={(y2-y1)/(x2-x1)} where
y2=16ma; y1=12 ma; x2=375 mmwc; x1=0 & C is 12ma at 0 mmwc
so y= (4/375)*x + 12
in order to get correct flow change the transfer function to square root in Tx
Is This Answer Correct ? | 2 Yes | 0 No |
What is hp & mp seperator .& what is its working principle ?
-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.
how to make a calibration for differential pressure
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?
Anybody know how to create a ladder programme for power switch in TV remote without using counter... ie TV can be turn on and turn off using single push button switch... on pressing the switch first time TV turn on and hold the on state till i press the switch again, and after TV turn off.
What is the purpose of MATLAB?
pls suggest suitable MOC of diaphragm for pressure measurement of UREA grade solution service fluid.
How many interlocks at turbine side?
What is difference between Isolator and Barrier ?
Explain the difference between differial pressure & delta pressure?
What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process