A motor is taking 15 Amps at no load and 60 Amps at full load.
and a valve has to open 10% at full load and 80% at no load.
How to draw ladder logic.(PLC).
Answers were Sorted based on User's Feedback
YOU NEED A CURRENT TRANSDUCER AT YOUR MCC WHICH CAN GIVE YOU
THE 4-20mA SIGNAL WITH 0 TO 70Amps. proportionally.
USE LESS THAN & GREATER THAN BLOCK LOGIC FOR OPEN & CLOSE
THE VALVE.
| Is This Answer Correct ? | 7 Yes | 0 No |
U dont need any plc logic for such application since u can
do this project with the help of simple transducer which
will gives the mA o/p with respect to ur Amps. & just i/p
converter which will help u to open ur positioner valve.
| Is This Answer Correct ? | 5 Yes | 0 No |
what is cascade system ?
why we use only 4-20 ma signal as AI and not 0-20 ma?
2 Answers Honeywell, Oil and Gas Jobs,
What are the cable come out from the paddle type flow sensor.and how is further connections
It is desired to reduce effect of 50Hz pick up in a thermocouple measurement. If a third order LP filter is used for this, what should be its cut off frequency, if gain should be 0.001 at 50Hz.
WHAT IS DIFFERANCE BETWEEN INSTRUMENT AND EQUIPMENT
which is type of thermocouple is used to measure 1000deg?
define COMPENSATION??
what is cascade controller ?
if I did short to both AO connections, channel will burn or what? m sure in AI it will damage to channel. But what will happens in AO?
how can we calibrate RADAR LEVEL transmitter 0% to 100%
3 Answers Chevron Phillips, Honeywell,
What is Cryogenic?
what is rtd
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)