what is the calibration standard for pressure and differential pressure
transmitters?
Answer / jaffer
differential pressure transmitters:
1.both side applied a pneumatic pressure in the h.p&l.p side
check the response on the dp cell.
2.equal pressure on the both side and then transmitters shown
a zero value.
3.upper range value(URL)on the h.p side 10,000mmwc or 1kg/cm2. this value depend on process reqirement.
4.lower range value(LRL)on the l.p side 0 mmwc or 0 kg/cm2.
5.And then change value&change the tag no.
6.check the states of the transmitter. by the help of field calibration devices.
pressure transmitters:
1.the pressure transmitter is only one physical quantity sensing input&applied a input and then same 2,3,4,5,6steps.
| Is This Answer Correct ? | 5 Yes | 0 No |
Explain the difference between plc and cnc?
CAN WE CALIBRATE LEVEL TRANSMITTER USING HART COMMUNICATOR WHEN WATER LEVEL IS PRESENT IN THE BOILER SHELL?
Technician A says that a fuel tank sending unit will have a high resistance only when the tank is full. Technician B says that its resistance when the tank is full depends on whether the sending unit is designed for use with a bimetallic gauge or with a magnetic gauge. Who is correct?
what is the process to make control schematic ?
key phaser where is use and work
with the help of suitable diagrams different types of control valves
p=hdg,please explain these parameters?
why level transmitter input is given 4to20ma
Yokogawa dcs normally where will change 4-20 MA to DC voltage( node or I/o cards?)
why 4 to 20 ma? why cant some other range?
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,
rtd principle?thermocouple principle?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)