how many safeties should be present in boiler?what are they?
Answers were Sorted based on User's Feedback
Answer / bhola shnaker
there are 2 to 6 numbers of safety valves (SVs) on the boiler.
Around 2 Nos on Drum, of one high and one low setpoint.
Around 2 Nos on Superheater Steam Line of one high and one low setpoint.(but less then Drum SV setpoint, to avoid starvation of SH main steam line)
around 2 Nos on reheater line (if reheater is provided)
Apart from it 1 No of EMRV on the HP superheater line, setpoints below that of Safety valves of the lines.
Also we have Relief valves on he HP econimiser, which acts as a Over protection valve (against Pressure)
Remember SVs are Differnt from Relief valves, as RVs are used on liquid whereas SVs are used on Steam line.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / arun
Totally 9 SV are There
Drum - 3 ( left side-1 , right side-2 )
SH Outlet( MS Line ) - 2
RH Inlet - 1
RH Outlet - 3
This is for BHEL 210MW Boiler
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / powerplant.calculations
Boiler interlocks:
1-High & low drum level trip
2-High furnace draught trip
3-Safety valve
4-Boiler explosion vents
Also refer following link to get more information on Boilers
https://www.powerplantandcalculations.com/2020/06/why-how-these-in-boilers.html
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pandian
only 6 safety valves used in reheater boilers normally small capacity boiler used 4 safety valves
| Is This Answer Correct ? | 0 Yes | 1 No |
Why attemperation is required in HRSG in a combined cycle power plant?
why HT motor star not grounded?
Why the steam Turbines are Designed Higher side compare to Alternator
why do you consider yourself a suitable candidate for this position
0 Answers Amazon, Eskom, Nabard,
if suppose boiler has high heavy tube leakage, so in which time we feed the water in a boiler. can we stop the feed water at particular combustion temperature.
If a pump has "N" no .of conections in the discharge. If a connection has a heavy leakage. Then it's motor current get affected or not??
How do you consider that you can improve and what assistance do you need to achieve this
What happens if lizard comes in a MOCB
whats plant?
how to differentiate between "ALL fuel lost" and "All Fuel Lost" in Boiler MFT condition?
DCS marshaling Cabinet Power supply can be replace during plant running time? Answer Yes it is possible. I am talking about the controller and cards power supply modules. They are always redundant and connected through diode so that if one power supply fails the other can take the charge immediately.so it is possible to replace one of them in running plant if the other one is healthy. MY question is how switching done.
Calculating Seawater consumption for SWFGD system
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)