In Megger which types of test we can do ? and How it works? How to use?
Answers were Sorted based on User's Feedback
Answer / t. krishna moorthy
insulation resistance with respect conductor to ground &
between two conductors insulation value.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / nandagopan
for 3 phase motors megger is used to test the insulation
resistance of motor winding.phase to earth(winding to body)
must be greater than 1 mega ohm.
Is This Answer Correct ? | 1 Yes | 0 No |
how can tell us the AC indoor or outdoor which Tr and formulls
what is the difference between interconnection and intraconnections in the circuit diagrams
what is first pole to clear factor
what is ceiling voltage in an exciter?
1 Answers KEPCO Energy Service Company,
Describe the test procedure to determine the vector group
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
0 Answers Enmas, Michelin, Reliance,
if we convert kw into Ampers,which one formula use by us,pls tell me?
How to measure the earth resistance value in a concrete pavement(flood light area)?
What is the cause for a blown fuse in one phase of primery side(HV) of a three phase transformer( 4169v-460v) in the time of closing its supply breaker. There is no load on the secondery side of the transformer in this moment.
How power is transferred from one winding to another in an auto-transformer? A) electrically B) magnetically C( both a & b D) neither of above
what do you mean by earth fault in transformer?
what is Insulation monitoring device. where it is used? (in switchgear room or control panel or in field equipment)