Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line
to get
20mA O/P by adjusting SPAN ?
Answer / carl_ellis
You can do whatever you want to with the span adjustment,
but what do you think the results are going to be?
10000:100 is a 100:1 turndown.
Which flow meter technology that uses an analog adjustable
20mA span has 100:1 turndown?
Which flow meter technology has a HART configurable URV with
a 100:1 turndown?
Flow meter accuracy curves ALWAYS bend exponentially upwards
towards increasing uncertainty as the flow approaches zero
low flow. The lower the flow, the greater uncertainty.
Where do you suppose 100 Lph is on the accuracy curve of a
meter designed for 10000 Lph?
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
Q1]IF THE RANGE FOR FLOW IS -35 TO 125 WHAT WILL BE THE SPAN FOR ABSOLUTE AND FOR NORMAL? Q2]HOW TO CALIBRATE CAPILLARY TYPE LT? Q3]HOW MANY ERROR CALCULATIONS ARE THERE USED IN PROCESS INDUSTRIES? Q4]HOW TO CALIBRATE TEMPERATURE TRANSMITTER? Q5] HOW TO CALIBRATE LEVEL TROLL AND HOW TO CONNECT? Q6]PLEASE TELL ME THE BASIC FOR INSTRUMENTATION WHICH IS APPLIED FOR CALIBRATION AND FOR ALL? PLEASE MAIL THE ANSWER TO honest_yes@yahoo.in
how many parts of valve positioner?
please help me to get the below mentioned quires,which i have to submit for my client.[INSPECTION TEST PLAN] 1]I.T.P for Calibration of all instrument. 2]I.T.P for SS tubing. 3]I.T.P for Fire & Gas devices. 4]I.T.P for CCTV & telecommunication. 5] I.T.P for loop checking.
Tyes of interface level measurement and how to use that technique for interface level measurement,
why is negative range given to measure the steam drum level
Different between control valve and mov
What is Trim?
What is the working principle of the magnetic meter?
Explain the key components of control loop?
can we control operation of PLC from operator station?
How do you identify between actual alarm and false alarm in a Temperature Transmitter in SCADA based Control System
difference between null and deflecting instrument.