Answer / sudipto jena
hello,this is sudipto,from rourkela
In the above question ,there is a alphabet and then two
digits are present in the code.The digits are for current
carrying capacity. Here the mcb can carry 32 A of ac current
safely.
Now the alphabet stands for the type of mcb, taking
overloading and tripping time of mcb in account.
A for 1.5 to 2 times of overload current and tripping time
about 70 ms
B for 3 to 5 times of overload current and tripping time
about 50-60 ms
C for 5 to 10 times of overload current and tripping time
about 35-45 ms
D for 10 to 15 times of overload current and tripping time
about 20 ms
Generally for residential wiring we use D type for the
purpose of protecting from short ckt fault.
Is This Answer Correct ? | 37 Yes | 6 No |
Answer / manikandan krishnan
First Digit A denotes tripping Curve and second two digits are rating of the breaker..Normally C curve withstand 7-10 time of FLC,D - 10-14 TIMES AND B CURVE is 3.2-4.8 TIMES OF FLC.
Is This Answer Correct ? | 12 Yes | 4 No |
how are reversing the direction of dc motor
why the generating voltage in India is 11kV or why is it be transmitted as multiples of 11
34 Answers ACC, Bhel, ECI Engineering and Construction, NTPC, SBL, Senthur Power Services,
What is Toroid?. What is the difference between toroid and Current Transformer
how much mininmum length required to conduct a DC Hipot Test on 33kV AC Cable with 45kV DC? Is it 20meter or Less then 20?
why protection meter is always connect to star
How to size the Neutral grounding resistor?
WHAT IS REACTIVE POWER?
Tell me about Simence PLC 'BLOCK'.How many types and what for.
Why field resistance is greater than the armature resistance in dc mechine
1 Answers Cape Peninsula University of Technology,
Where the excitation is given either stator or rotor in actually in power plants?
Tell me harmfull effects of over voltage,under voltage,spike,surge,transient & noise.
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation