how to calculate Transformer loss?
Transformer losses are winding losses[copper or aluminum
conductor losses] Pcu and steel
laminate core losses Pfe Ptot=Pcu+Pfe
If you would know the resistance per phase at working
temperature[R] you could calculate winding losses
Pcu=n*Irat^2*R [n=no.of phases;Irat=transformer rated
current].
In order to calculate laminate core losses you need to know:
unit losses of the steel laminate[w/lb or w/kg],total core
weight [lb or kg].
Pfe=[w/lb]*weight[lb].
In order to state the unit losses[from Manufacturer
Catalogue] you'll need magnetic flux density[B[wb/m^2 or
gauss/inch^2] and the current frequency[50 Hz or 60 c/sec].
| Is This Answer Correct ? | 1 Yes | 0 No |
what is relay
how we calculate the motor rating of pump for water suction ?its any formula for that plz give thank u
Help need in transformer !? Hello Friends The parameters of 2300/230 v 50hz t/f is R1=0.286 ohm R`2=0.319 ohm Rc=240 ohm X1=0.73 ohm X`2=0.73 ohm Xm=49.2 ohm Secondary Load impedance ZL=0.387+J0.29 solve the exact equivalent circuit with normal voltage across primery.. I know every thing but i cant find CURRENT I1=? and I`2=? Please help me give solution or only Formula please please...
What is servo motor and what are different types of servo motor
which one cable has a more resistance.A big or small
WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS
why there is a phase difference between line voltage & phase voltage ?
what is the purpose of supervision relay coil
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase), before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
what's prime importance of protection in electrical system.if protection system don't work properly what can happen in electrical system?
1.what is surge 2.what is lightning 3.what is switching 4.difference between surge,lightning,switching used in power system 4.definition of surgearrestor,lightningarrestor 5.adv and disadv of surgearrestor,lightningarrestor 6.uses and purpose of surgearrestorand lightning arrestor 7.block dia of surge arrestor 8.blockdiagram of lightning arrestor 9.operation and working of surge arrestor and lightning arrestor 10.basic formula of surgearrestor and lightning arrestor 11.basic diagram of surge arrestor and lightning arrestor
1 Answers Crompton Greaves, Framo, L&T,
The error in a single phase energy meter where pressure coil lags behind applied voltage by 88 degrees and pf is 1) upf 2).5lag
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)