if the synchronizing b/w
generator and busbar not
complete and we close the
out going circuit breaker
of generator then what
happen ?
Answers were Sorted based on User's Feedback
Answer / sheikh
if synchronization b/w generator and busbar would not be
completed and if you close the out going CB then generator
have gone to over current tripped or reverse power tripped
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / hamuel vilho
the generator winding wire will become hot and get broken which lead to linkage and it will get damaged,NB it is very expensive to repair winding wire, never try to close the circuit breaker if they are not in the same phases, frequency,
| Is This Answer Correct ? | 1 Yes | 0 No |
IF the synchronization does not complete and if you close a cct breaker a severe arcing may occur and generator will trip instantaneously. Because the Generator sides voltages and bus side voltages do not match. To match the volatges following has to satisfied.
1. voltage magnitude
2. phase angle difference - 0
3. phase sequence - same
So at this condition there might be present voltage or phase angles or phase position mismatches. Say for example there exists a voltage magntude mismatch of 1 kV and when you close the cct breaker contact points have that voltage across them and this will cause severe current through contact points of breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kk
First of all check sync relay will not permit to sync due to control ckt configuration, perhaps if it did then gen bkr would tripped in reverse power (32P relay) acted.
| Is This Answer Correct ? | 0 Yes | 0 No |
What the difference between ac and dc inductor an capacitor
why the pf of semiconductor device is improved the electrical devices
I have tow 200 KVA UPS, both are in parallel mode.My question is that, both are running on battery when power fail, if one of them fail (Eg rectifire fails or some other reason), at thet time reverse power will come to faild ups if it comes then it will harm to failed ups or not? if not then how it protects to faied ups????????????????
What is TR of AC?
The earth pin of some three pin plugs are seen split. why?
why neutral should connect to earth in delta-star type transformer
Explain the fundamental difference between emf (electro motive force) and pd (potential difference) ?
please send me previose rrb junior engineer qustion papers
why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)
why we are using star connection and delta connection? difference?
A 400 V, 50 Hz, Δ connected synchronous generator has a field reactance of 0.1 Ω and armature resistance of 0.015 Ω. At full load, the machine supplies 1200 A at 0.8 pf lagging. Under full-load conditions, the friction and windage losses are 40 KW and the core losses are 30 KW. What is the machine’s overall efficiency? Ignore any field circuit losses.
why star 2 delta or delta to star preferred mostly then star to star and delta to delta ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)