if the synchronizing b/w
generator and busbar not
complete and we close the
out going circuit breaker
of generator then what
happen ?
Answers were Sorted based on User's Feedback
Answer / sheikh
if synchronization b/w generator and busbar would not be
completed and if you close the out going CB then generator
have gone to over current tripped or reverse power tripped
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / hamuel vilho
the generator winding wire will become hot and get broken which lead to linkage and it will get damaged,NB it is very expensive to repair winding wire, never try to close the circuit breaker if they are not in the same phases, frequency,
Is This Answer Correct ? | 1 Yes | 0 No |
IF the synchronization does not complete and if you close a cct breaker a severe arcing may occur and generator will trip instantaneously. Because the Generator sides voltages and bus side voltages do not match. To match the volatges following has to satisfied.
1. voltage magnitude
2. phase angle difference - 0
3. phase sequence - same
So at this condition there might be present voltage or phase angles or phase position mismatches. Say for example there exists a voltage magntude mismatch of 1 kV and when you close the cct breaker contact points have that voltage across them and this will cause severe current through contact points of breaker
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kk
First of all check sync relay will not permit to sync due to control ckt configuration, perhaps if it did then gen bkr would tripped in reverse power (32P relay) acted.
Is This Answer Correct ? | 0 Yes | 0 No |
why high speed tripping relay is used in protection circuit why not normal relay
Why cannot we insulate HT over head cable to avoid ionization of air around the HT Cable?..By this we can minimise corona loss also..
what is the main parts of transformer? how it is functioning? pls giv the ans briefly.
what are the types of cooling systems used in motors?
What is the problem of internal failure in ship engine telegraph system norcontrol?
What is the advantangeous over SFU (switch fuse Unit) & FsU (Fuse Switch unit) which one is better & application of Both?
What is the value of specific gravity in charged lead acid batteries.
what will happen if ac power supply is given to the rotor of an alternator
WHAT MEANT BY MCC PANEL?
if field current decreases how can the speed increase in the unloaded dc series motor
What is the type of feedback used in an op- amp schmitt trigger?
Which types of gate insttaled in static switch. Please give me answer.