Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


if the synchronizing b/w
generator and busbar not
complete and we close the
out going circuit breaker
of generator then what
happen ?

Answers were Sorted based on User's Feedback



if the synchronizing b/w generator and busbar not complete and we close the out going circuit ..

Answer / sheikh

if synchronization b/w generator and busbar would not be
completed and if you close the out going CB then generator
have gone to over current tripped or reverse power tripped

Is This Answer Correct ?    3 Yes 0 No

if the synchronizing b/w generator and busbar not complete and we close the out going circuit ..

Answer / hamuel vilho

the generator winding wire will become hot and get broken which lead to linkage and it will get damaged,NB it is very expensive to repair winding wire, never try to close the circuit breaker if they are not in the same phases, frequency,

Is This Answer Correct ?    1 Yes 0 No

if the synchronizing b/w generator and busbar not complete and we close the out going circuit ..

Answer / milinda4p

IF the synchronization does not complete and if you close a cct breaker a severe arcing may occur and generator will trip instantaneously. Because the Generator sides voltages and bus side voltages do not match. To match the volatges following has to satisfied.
1. voltage magnitude
2. phase angle difference - 0
3. phase sequence - same
So at this condition there might be present voltage or phase angles or phase position mismatches. Say for example there exists a voltage magntude mismatch of 1 kV and when you close the cct breaker contact points have that voltage across them and this will cause severe current through contact points of breaker

Is This Answer Correct ?    0 Yes 0 No

if the synchronizing b/w generator and busbar not complete and we close the out going circuit ..

Answer / kk

First of all check sync relay will not permit to sync due to control ckt configuration, perhaps if it did then gen bkr would tripped in reverse power (32P relay) acted.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What the difference between ac and dc inductor an capacitor

0 Answers  


why the pf of semiconductor device is improved the electrical devices

0 Answers  


I have tow 200 KVA UPS, both are in parallel mode.My question is that, both are running on battery when power fail, if one of them fail (Eg rectifire fails or some other reason), at thet time reverse power will come to faild ups if it comes then it will harm to failed ups or not? if not then how it protects to faied ups????????????????

1 Answers  


What is TR of AC?

11 Answers   Carrier, Reliance,


The earth pin of some three pin plugs are seen split. why?

1 Answers  


why neutral should connect to earth in delta-star type transformer

4 Answers  


Explain the fundamental difference between emf (electro motive force) and pd (potential difference) ?

0 Answers  


please send me previose rrb junior engineer qustion papers

0 Answers   RRB,


why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)

0 Answers  


why we are using star connection and delta connection? difference?

5 Answers  


A 400 V, 50 Hz, Δ connected synchronous generator has a field reactance of 0.1 Ω and armature resistance of 0.015 Ω. At full load, the machine supplies 1200 A at 0.8 pf lagging. Under full-load conditions, the friction and windage losses are 40 KW and the core losses are 30 KW. What is the machine’s overall efficiency? Ignore any field circuit losses.

0 Answers   VECL,


why star 2 delta or delta to star preferred mostly then star to star and delta to delta ?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)