Answer / sheikh
if synchronization b/w generator and busbar would not be
completed and if you close the out going CB then generator
have gone to over current tripped or reverse power tripped
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / hamuel vilho
the generator winding wire will become hot and get broken which lead to linkage and it will get damaged,NB it is very expensive to repair winding wire, never try to close the circuit breaker if they are not in the same phases, frequency,
| Is This Answer Correct ? | 1 Yes | 0 No |
IF the synchronization does not complete and if you close a cct breaker a severe arcing may occur and generator will trip instantaneously. Because the Generator sides voltages and bus side voltages do not match. To match the volatges following has to satisfied.
1. voltage magnitude
2. phase angle difference - 0
3. phase sequence - same
So at this condition there might be present voltage or phase angles or phase position mismatches. Say for example there exists a voltage magntude mismatch of 1 kV and when you close the cct breaker contact points have that voltage across them and this will cause severe current through contact points of breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kk
First of all check sync relay will not permit to sync due to control ckt configuration, perhaps if it did then gen bkr would tripped in reverse power (32P relay) acted.
| Is This Answer Correct ? | 0 Yes | 0 No |
How to perform a DC resistance test In Alternator and their proceduces?
what is electric traction?
Consider three heater bank connected in 3 phase star with neutral.Each heater bank connected in each phase.So each phase get 230 volts supply.my question is,during balance condition, current flow in neutral or Not
Define damping ratio.
How much Fault current can be contributed by a motor?
It is advisable 2 use auto-transformer if transformation ratio is-a)110KV/11KV,b)230kv/110kv,c)110kv/66kv,d) 400kv/230kv
what are all the components required to assemble solar panel other than pv cell?
If a 3 phase transformer is a 500 kva using the formulae 500kva= 500000/433 x 1.732 = 666.71amps does this mean that each phase on the secondary side is 666.71
what meant by Locked Rotor Current ?
What are hrc fuses and where it is used?
Are you connected Transformer neutral eathing with it's body earthing or earthing met of switch yard.? Yes or No ? why ?
what is the main function of capacitors in mccs.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)