Answer / subbarayalu
The normal method
of expressing transformer impedance is as a percentage voltage drop in the
transformer at full-load current and this reflects the way in which it is seen by
system designers. For example, an impedance of 10% means that the voltage
drop at full-load current is 10% of the open-circuit voltage, or, alternatively,
neglecting any other impedance in the system, at 10 times full-load current, the
voltage drop in the transformer is equal to the total system voltage.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / anonymous
It is because three phase system is most economical out of all possible polyphase system configurations...that's it...
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sokib
why did electric polyphase system commonly using three phase
system? is there any electrical system more than three phase
system?
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / 7anoter4
Usually group of transformers presents the same short-
circuit reactance in %
For instance, for S[ rated power] up to 2500 [to 3000] kVA
the percent reactance will be vk%=4-8. Ohmically calculated
reactance will be V^2/S*vk%/100 [ V=rated voltage].
For V=10 kV and vk%=6 for S=500 kVA Xk=10^2/0.5*6/100=12
ohm
For V=6 kV and vk%=6 for S=3000 kVA Xk=6^2/3*6/100=0.72 ohm
As one could see it is more convenient to consider only
vk% instead of ohmic reactance
| Is This Answer Correct ? | 0 Yes | 1 No |
is tree is a good conductor and it may be used for conductor?
how the 12 pulse rectifier is made?
8 Answers Engineers India Limited,
What is online and offline ups? how does it works?
what is maximum demand.
Why there is restriction to generated voltage to certain limit for example (now 18kv) ?
3 Answers College School Exams Tests,
why we use low kv lightining arrester in line for example 9 kv using in 11kv
What is Load sharing of Transformer ?
what is the use of neutral?
What are the main advantages of generalized error co-efficients?
What is the formula for calculating impedance of transformers connected parallel at fault level 50KA?
In pakistan appliances work on 220v at 50hz and in us appliances work on 110v at 60hz what is basic theory to explain it
can any one list the class-a, class-b & class-c trips of power generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)