why transformer impedance measure in % (percentage)
Answers were Sorted based on User's Feedback
Answer / subbarayalu
The normal method
of expressing transformer impedance is as a percentage voltage drop in the
transformer at full-load current and this reflects the way in which it is seen by
system designers. For example, an impedance of 10% means that the voltage
drop at full-load current is 10% of the open-circuit voltage, or, alternatively,
neglecting any other impedance in the system, at 10 times full-load current, the
voltage drop in the transformer is equal to the total system voltage.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / anonymous
It is because three phase system is most economical out of all possible polyphase system configurations...that's it...
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sokib
why did electric polyphase system commonly using three phase
system? is there any electrical system more than three phase
system?
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / 7anoter4
Usually group of transformers presents the same short-
circuit reactance in %
For instance, for S[ rated power] up to 2500 [to 3000] kVA
the percent reactance will be vk%=4-8. Ohmically calculated
reactance will be V^2/S*vk%/100 [ V=rated voltage].
For V=10 kV and vk%=6 for S=500 kVA Xk=10^2/0.5*6/100=12
ohm
For V=6 kV and vk%=6 for S=3000 kVA Xk=6^2/3*6/100=0.72 ohm
As one could see it is more convenient to consider only
vk% instead of ohmic reactance
Is This Answer Correct ? | 0 Yes | 1 No |
can anybody give me current carrying capacity of cables e.g size of cable in sq.mm & its current capacity both alluminum & for copper
Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?
If current and resistance in a circuit is increased by 20%, what will happen to its voltage drop??
How Many Safety of Transformer
what happen if drive input fail momentry at 48.5 HZ frequency?
discuss thyrister convertor type of AVR.
is oil viscosity affect on motor current?
transformer losses
freuency meter
Distribution transformer we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral,we can not connect separate body earthing pit to other earthing pit but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), is this safe for transformer and other equipment?
what is the different betweem earthing and neutral?
Is there any difference of regulation of transformer, alternator , transmission line, if yes, what is it?