What is the function of Antipumping Relay and Lockout Relay?
Answer / avdhesh
Antipumping Relay : It is generaly used in series of
closing coil of breaker. The function is to cut off the
supply of closing coil immediately after closing of
breaker. This is required as coil is not designed for
continous rating.
Lockout relay : This is also used in closing ckt of
breaker. This is basicaly latched relay which inihibit the
closing of breaker for defined time if relay is operated.
Lockout relay can be self reset or manual reset (choice)
after definite time.
Is This Answer Correct ? | 1 Yes | 0 No |
which mm cable should be used for 1.hp immersible pump motor for the distance of 330 metres?
in traction which type of supply are used
15 Answers APGenco, Construction,
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise carrying amps rating.Please give the solution with a good example.
If the ceiling fan is on slow speed, does it consume less electricity?
How does the sensitive earth fault protection provided by cbct for motor can help in reducing the size of cable used to supply the motor?
Explain why the Voltage drop will happen in 3 Phase line?
What is the maximum load an electric engine can pull??
What is differnce b/w tie breaker and bus coupler?
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
why most of the induction motors are delta connected?
I HAVE 2 nO'S OF SYSTEMS, HOW MUCH UPS CAPACITY REQUIRED ALONG WITH 400WATTS ANOTHER LOAD? PLEASE GIVE THE FORMULA?
sir, why alternator output is connected to delta side in to generating transformer? any reasion?