My ups output shows 230 v between phase and neutral,but show
zero between phase and earth.Is the system/installation is
correct.If not what will be the possible reasons
Answers were Sorted based on User's Feedback
Answer / nck
correct.it will show output between phase and earth only and only in faulty condition not in normal.if there is fault and still not output between ph-earth then your earthing is not properly done.
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / hemalatha
earthing point where you checked may not be perfect.
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / akot
there should be out put between phase and earth unless the
earth is also having current or improperly done, to rule
out if your earth is having current measure earth to
neutral.
Is This Answer Correct ? | 0 Yes | 2 No |
what are the differenc between vcb and sf6 breakers
what is the formula to find out how many amps generater takes running on full load.
Disadvantage of leading power factor
Can a dc motor works as a dc generator. If yes , then how?
What is the causes Power Factor become leading and what is the effect of Electrical system ?
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
1.what is use of isolation transformer. 2.Differance between KWH,KVAH,KVARH,KVA. 3.Main use of the CT and PT.
wat is the advantage of increse in frequency?how the powersupply range decreses as the frequency increses?like in america,it uses 110 ac and 60 hz?
IF WE SELECT THE 60H FREQUENCY IN INDIA WHAT WILL THE GOOD AND BAD EFFECT ?
What happens when the field of an alternator connected to infinite bus is suddenly removed?
when a motor is connected in parallel with the existing motor the pf will change or not?
Will transformer heating be approximately the same for resistive, inductive or capacitive loads of the same VA rating? Explain.