My ups output shows 230 v between phase and neutral,but show
zero between phase and earth.Is the system/installation is
correct.If not what will be the possible reasons
Answers were Sorted based on User's Feedback
Answer / nck
correct.it will show output between phase and earth only and only in faulty condition not in normal.if there is fault and still not output between ph-earth then your earthing is not properly done.
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / hemalatha
earthing point where you checked may not be perfect.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / akot
there should be out put between phase and earth unless the
earth is also having current or improperly done, to rule
out if your earth is having current measure earth to
neutral.
| Is This Answer Correct ? | 0 Yes | 2 No |
can we run the home fan both clock and anticlockwise direction
What are Line losses and how can be it minimized/controlled.?
on a three-winding transformer relationship delta-delta-star, on third winding why the relationship is a star? what are the advantages and disadvantages? Thank you and please help
directional relay is typically used to respond in fault condition who it can be used just as reverse power protection which purely senes direction reversal to operate a circuit breaker?
What is the fault or needs to be done when frequency in ac drives is not changing?
is any body explain me why return current in three phase power system is less then in a red, yellow, blue phases??? as we know Ir+Iy+Ib=In then why nutral wire has less then phase current????
What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to reconfirm its base capacity.
what is JE exam?
i want to know about psu exam eligibility critaria?
where is core-type and shell-type construction suitable for transformers ?
A 6-pole, 50 Hz, 3-phase synchronous motor and on 8-pole, 50 Hz, 3-phase slip-ring induction motor are mechanically coupled and operate on the same 3-phase, 50 Hz supply. If they are left open-circuited, then the frequency of the voltage produced across any two slip rings would be
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)