what is the differance between normal bybass & maintenance
bybass in UPS?
Answer / ruben
UPS has internal bypass and used if in case there is some
problem within the UPS, ie. overload. the load will be
automatically fed from the bypass circuit. the maintenance
bypass is an external circuit or feeder that is use to feed
the load (bypassing the UPS). this will allow the user to
remove completely remove the UPS from the network/system for
maintenance or replacement.
| Is This Answer Correct ? | 2 Yes | 0 No |
Why dnt we generate 5-ph or 7-ph supply like as 3-ph supply
What is the difference b/w RMU & substation
why do we generate sinusoidal ac?can we generate some other waveforms by alternators?
why swityard is necessrry requirement in any bis power distributin systems?
please send me last 5 year interview questions
what mean by analog ,digital,numerical meters and relays? say the example?
Why short circuit calculation is not required in LT cable sizing and requiredin HT cable sizing only
What is difference between earth leakage relay and restricted earth fault relay ?
what is ICU and ICS in breaker ratings
1. what is exciting winding, rotor winding, startor winding. and how it works? in ac generator
we know that dc motors are more superior then three phase induction motors in torque generation though they are not much used in industries why?
how to can we synchronize different capacity of DG sets.60kva& 250kva?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)