what is the differance between normal bybass & maintenance
bybass in UPS?
Answer / ruben
UPS has internal bypass and used if in case there is some
problem within the UPS, ie. overload. the load will be
automatically fed from the bypass circuit. the maintenance
bypass is an external circuit or feeder that is use to feed
the load (bypassing the UPS). this will allow the user to
remove completely remove the UPS from the network/system for
maintenance or replacement.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is work of CTPT in 33/11kv Substation
HOW isolation transformer works.
What is the AVR in DG & its functios
how to measure genset CT coil range?
71ohm,111ohm,95ohm,179ohm in calculate the total ohm in series circuit
where is the primary of CT??
During FEED, you will have all the information with regards to cable. How will you calculate the MTO for MV and LV Cables? what are your considerations?
why phase always came one direction in 5pin socket(right hand or left hand) which direction and why..........?
electrical ques
What are RMU yard Safety Operating Procedures
how the earthing point or earthing is taken for ships and airplanes?
In case of delta/delta transformer if the one phase is blown out then what will be secondary line voltage ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)